Lateral thinking Wilko.Oh dear, thought I had a handle on this one ... more to think about .
Discuss EICR or Minor Works??? in the UK Electrical Forum area at ElectriciansForums.net
Lateral thinking Wilko.Oh dear, thought I had a handle on this one ... more to think about .
Really bizzare..putting an RCD on a shower when there wasn't one there before..what was I thinking??Overall it seems a bizarre thing to have done.
You haven't wired a new circuit, you have altered an existing circuit MNWThis is a EIC in my opinion. The supply to the shower isolator is now a distribution circuit.
Also the shower isolator did not burn out because there was no RCD installed.
I agree, what were you thinking. Straight forward replacement switch with a departure on the Minor Works additional rcd protection not provided, existing circuit.Really bizzare..putting an RCD on a shower when there wasn't one there before..what was I thinking??
You haven't wired a new circuit, you have altered an existing circuit MNW
Sorry but I like to add an RCD if it's possible.I agree, what were you thinking. Straight forward replacement switch with a departure on the Minor Works additional rcd protection not provided, existing circuit.
Sorry but I like to add an RCD if it's possible.
No comment Wilko, rest easyOooo now you've done it
No comment Wilko, rest easyOooo now you've done it
What would you enter on this EIC then as work done?EIC according to the NIC! Thanks for your replies.
Why?
At a guess "because it needs RCD Protection"Why?
I know, what's that got to do with my post though?An EIC is not just for new circuits.
At a guess "because it needs RCD Protection"
He never said that. He said "where ever possible".
Are you referring to post 28 "i would like to add an RCD if it's possible"He never said that. He said "where ever possible".