Discuss EICR or Minor Works??? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
39
Just a quick one.. I have been to a job today where the shower isolator switch had burnt out, as it wasn't RCD protected I replaced the switch with a 1 way consumer unit with an RCD.

My question is..do I need to do a full EIC or would a minor works do?

Cheers
 
Last edited:
An EICR is a report on an installation

A MWC is a certificate to confirm changes or replacements to existing circuits ...

An EIC covers new circuits ...

What exactly did you do?
 
Is this a troll post?
An EICR is a report on an installation

A MWC is a certificate to confirm changes or replacements to existing circuits ...

An EIC covers new circuits ...

What exactly did you do?

Shower isolator had burned out and was faulty.

The existing shower circuit wasn't RCD protected so replaced the shower isolator with a 1 way consumer unit which had an RCD.
 
Shower isolator had burned out and was faulty.

The existing shower circuit wasn't RCD protected so replaced the shower isolator with a 1 way consumer unit which had an RCD.
So you altered an already existing circuit correct? MNW can I clarify my comment and explain my conclusions, before the keyboard warriors rip me to shreds?
My thoughts are that the OP has replaced the damaged Shower isolator with a 1 way CU incorporating a RCD, he has not wired a new circuit, neither has he changed the CU at least that's how I understand what he has done. Perhaps I have miss read, but I don't think so, awaiting the deluge of abuse.
 
Last edited:
So you altered an already existing circuit correct? MNW can I clarify my comment and explain my conclusions, before the keyboard warriors rip me to shreds?
My thoughts are that the OP has replaced the damaged Shower isolator with a 1 way CU incorporating a RCD, he has not wired a new circuit, neither has he changed the CU at least that's how I understand what he has done. Perhaps I have miss read, but I don't think so, awaiting the deluge of abuse.
PS I'm assuming the shower isolator was a wall mounted unit, NOT a ceiling switch.
 
Hi - the new "one way consumer unit which had an RCD" also had an MCB in it? This means (to me) there are now two circuits where there was one, each with its own earth loop and ADS times to be met.
Going with that analogy Wilko, if and I say if the OP had swapped the shower switch with a RCD / FSU instead of a small CU, would that not be similar, or the same as using a CU, after all, all he is doing is fusing down via the CB and adding a RCD? it's an imponderable I guess, which can/could argued either way, well that's how I tend to see it.
 
This is a EIC in my opinion. The supply to the shower isolator is now a distribution circuit.

Also the shower isolator did not burn out because there was no RCD installed.
You haven't wired a new circuit, you have altered an existing circuit MNW
 
Really bizzare..putting an RCD on a shower when there wasn't one there before..what was I thinking??
I agree, what were you thinking. Straight forward replacement switch with a departure on the Minor Works additional rcd protection not provided, existing circuit.
 
Why did you not fit an RCD in an enclosure the circuit should already have a protective device at the circuit origin so from that perspective I can see why members are saying EIC as a new circuit. I assume this existing burnt out switch was either outside the bathroom or in an adj cupboard. I agree with Pete on what is wrong with adding an RCD to increase the level of safety. It's MW but there would be nothing wrong with issuing an EIC just more paperwork.
 
You haven't wired a new circuit, you have altered an existing circuit MNW
I could kind of see where ESSEX was sort of coming from as switchgear rather than an accessory a subdistribution circuit has been made hence why saying EIC if an RCD in an enclosure replaced the isolation switch it would have been a straight MW.Still agree though can be MW for what's done.
 

Reply to EICR or Minor Works??? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
1K
Hi Everyone, This is my last question/post for tonight, promise. Please can I ask for a little advice on certificates as I am now questioning...
Replies
4
Views
954
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Replies
42
Views
2K
Hi guys, need a bit of advice, EICR was completed on the property which needed a new consumer unit and a few other bits like broken sockets and...
Replies
10
Views
880

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock