piggyitm

I've just been reading the Q & A guide and found that Q14 states

Q14. Is it acceptable to calculate (R1+R2) values when carrying out Condition Reports (PIRs), using measured loop impedance values?


No. In any event, it is not essential to measure (R1 + R2) values for a Condition Report.


Are they suggesting that you can skip the R1+R2 for a periodic?
 
Re: Electrical Saftey Council Periodic inspection of existing domestic and similar Q

In some circumstances yes.
For instance R1 + R2 does not have to be recorded or measured on radial circuits even during initial verification, if R2 is measured and recorded, or with PIRs if Zs at the furthest point is measured and recorded.
 
Last edited by a moderator:
Re: Electrical Saftey Council Periodic inspection of existing domestic and similar Q

If you have access to a previous PIR or EIC which has both R1R2 readings and Zs....it is acceptable to skip the R1R2 test and measure the Zs. As long as your measured value of Zs is substantially the same as on the previous cert it is reasonable to assume the R1R2 will be as well.
If not,as above...you will have to measure and record either R1R2 or R2.
 
Re: Electrical Saftey Council Periodic inspection of existing domestic and similar Q

its not all its cracked up to be in the 'gate we have to do r1+r2 AND Ze cos there's never any certs
 

Reply to Electrical Saftey Council Periodic inspection of existing domestic and similar Q & A in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock