Discuss EV ultra cable, current carrying capacity in the UK Electrical Forum area at ElectriciansForums.net

jedisparks

-
Arms
Reaction score
76
Hi

Doncaster EV ultra cable:

Does anyone know what the current capacity of these cables is given particular reference methods?

The spec sheet just says 'Max current' 45amps (for the 4mm) but it doesn't state the reference method.

The manufacturer does have a very handy cable calculator tool but I'm not sure which category of cable the EV ultra falls into.

Many thanks
 
I’d take it as pvc/pvc or pvc/swa depending on structure.

It’s definitely not MICC, in conduit or trunking, or singles.
Then take the factors listed as installation method.
 
It's 90 degree thermosetting multicore so table 4E2A applies (subject to 90 degree operation being possible)
If its the armoured version then 4E4A.

Obviously if you're limited to a conductor operating temperature of 70C then you'd need to use the appropriate 70C tables.
 

Reply to EV ultra cable, current carrying capacity in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, go easy on me please, I've just returned to the trade, well I am about to, I received my Gold Card last Thursday. I've been gen'ing up for a...
Replies
4
Views
886
Had UKPN come out to a property recently to upgrade the main fuse from 60A to 100A but when they arrived they said that the supply cable which he...
Replies
9
Views
2K
Hi Guys Any one know the current carrying capacity of a 4mm 3 core single phase sy cable ran in a 20mm pvc conduit? Not sure of the right table...
Replies
2
Views
941
Just taken deilvery of an Electric Car (Mini Electric) and so doing some research into installing a charge point. Supply is a standard Single...
Replies
10
Views
4K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
446

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock