Search the forum,

Discuss Ferrule/bootlace Cu in the UK Electrical Forum area at ElectriciansForums.net

gazdkw82

-
Arms
Reaction score
739
iv just done my first ever CU board change. I had a qualified electrician with me. Now its all in and tested I want to tidy the terminations up abit and dress it up more. I was thinking of doing ferrule crimp/bootlace the conductors but im unsure if its bad practice to ferrule/bootlace solid conductors as apposed to stranded?

Also are the ratchet type crimpers better used?
 
Do you think it offers an advantage to fit ferrules to the solid cores? Also, bear in mind it adds another connection which is a potential weak point unless done correctly. Daz
 
There is no need to ferrule a solid conductor. They are not designed for such a task anyway. It would only offer the same strength of termination as a single solid conductor under a screw terminal. This would obviously not be as good as a properly doubled over and positioned solid conductor.
If you are thinking of aesthetics over mechanical and electrical soundness then you thinking about the job back to front.
 
There is no need to ferrule a solid conductor. They are not designed for such a task anyway. It would only offer the same strength of termination as a single solid conductor under a screw terminal. This would obviously not be as good as a properly doubled over and positioned solid conductor.
If you are thinking of aesthetics over mechanical and electrical soundness then you thinking about the job back to front.

No. Mechanical and safety comes first!
 

Reply to Ferrule/bootlace Cu in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock