Discuss Ferrule crimp tools part deux in the Electrical Tools and Products area at ElectriciansForums.net

pc1966

Esteemed
Arms
Reaction score
11,936
We often see folk asking about which crimp tool to buy/use so I decided to round up my collection and put them to the test. Ladies and gentlemen, here are the usual suspects:
ferrule-crimp-tools.jpg

Seems I cant post after the image? From the left we have:
 
Last edited:
First test was with 10mm tri-rated wire, fine stranded and all but the SWA tool could do this:

10mm-ferrules.jpg


Results were:
  1. For the simple Maun/RS tool it was easy but really needed two crimps for the 10mm ferrule.
  2. N/A [SWA tool limited to 6mm]
  3. The Engex crimp was tight, but lop-sided and stuck in the die
  4. The RS tool did a great job for this size (also for 16 & 25 elsewhere)
  5. The cheap Chinese tool work fine here
  6. The Expensive hex-die did a good crimp, but needed quite a firm hand force to complete.
 
Last edited:
Then 0.5mm fine stranded wire:
0.5mm-ferrules.jpg

This was the smallest for tools 1 & 2 and well within tools 5 & 6 rating
  1. Old RS/Maun tool fine
  2. SWA tool over-crimped, also getting easy to end up in gaps between correct crimp locations
  3. N/A (below range)
  4. N/A (below range)
  5. OK, moved a bit when pulled but not easily coming out
  6. Perfectly good
 
Finally 0.25mm fine-stranded wire (violet ferrules, not obvious in photo):
0.25mm-ferrules.jpg


This is within tools 5 & 6 range, but below tools 1 & 2
  1. Old RS/Maun was OK, moved a bit if pulled but stayed in
  2. SWA over-crimped significantly
  3. N/A
  4. N/A
  5. Cheap eBay failed, crimp looks OK but wire pulled out easily
  6. Expensive hex die was perfect
 
Conclusions?
  1. Well for all is basic appearance, the Maun tool is really good, but you need to get the right gap. However, adjacent gaps don't really lead to a stuck wire.
  2. The SWA tool is pretty rubbish. Having tried it a few times I really would bin it.
  3. Same for the Engex tool. While it does above the 16mm max of the Maun, it is not great.
  4. The RS tool is very good for all 3 sizes (10-25mm), but expensive
  5. The cheap eBay self-adjusting tool is great for 0.75-10mm and excellent value for money. Doubt it will last the 50,000 cycles RS/Pressmaster offer but at that price hardly worth complaining about. Not great at 0.5mm or below.
  6. The Pressmaster is good, but harder to use for the upper range and also expensive. If you are doing a lot of small ferrules (e.g. instruments, some control panel signal wiring) it makes sense, but hard to justify the total cost.
Over to you ladies and gentlemen to share your own experience....
 
Last edited:
I've got 2 cheap chinese ebay jobbies. Never had a problem with them. If you loose it you've not lost a lot of money.
 
I've got a pressmaster one, but I work in the water industry where failure is not an option ( unless it is caused by poor design and lack of maintainance because they are/were too busy creaming off profit until they got hit by massive fines).
 
Thanks for that pc1966...very interesting to see that trial.

I have a couple of decent ratchet crimpers for ferrules and terminals, but for fine wires, lighting etc I use a pair of CK plier-type crimpers for bootlace ferrules. They are ideal for the very small sizes, and being compact can be used in tight corners.
 
I also use the knipex pliers type, and like most things you get used to them and making sure it's in the right slot becomes automatic
My last Firm lots of people frowned on them preferring various ratchet types,

There were some connection problems in panels and wiring connected to them.
One of the Company Engineers decided to test them without anyone knowing
He had some previous extensive experience testing and calibrating crimp tools and connections for the Railway industry.
He picked panels which had been wired by different people with different tools

Most people were surprised at his report which basically said the same as Pc1966 tests
The pliers type were very reliable as long as they were a good make, manufactured to a DIN standard, not excessively worn, they were used properly.

The ratchet types did vary between makes, however some of the cheaper company supplied ones equalled the more expensive, which led to them being banned as there was too much variation in crimp quality
 
Be still my beating heart. I looked at this topic as it popped up when I started to create one titled "Cheap tools aren't good, good tools aren't cheap", because I have a one-off need to do some cord-end crimping of 4mm² - 16mm² tri-rated for a personal project.

eBay is awash with cheap Chinese POS Knipex look-alikes and I was going to ask if anybody knew if they were a POS in that they just aren't going to work, or a POS in that they aren't going to work for very long.

Looks like you've been a great help to me!
 
One thing to add is if you are using screw style terminals the crimp only needs to stop the ferrule easily coming off, as it gets further crushed by the termination. But if you use spring-loaded terminals like Wagos or some DIN rails, then you need a good crimp to get a good stable contact between the wire and the ferrule.
 

Reply to Ferrule crimp tools part deux in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Good morning all, I mainly work on boiler faults, and repairs. I sometimes have to install wireless thermostats, or renew the fcu switch. I’ve...
Replies
17
Views
3K
Hi any one use a sleeving tool ? If so what one and would you buy it again if you lost it ? I have this one 90110489 | Cable Sleeve Tool Plier...
Replies
14
Views
2K
Hiya, looking for a set of meter crimps, no malicious intent. They are to be used specifically for re-sealing after a fuse pull so the DNO keep...
Replies
28
Views
24K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock