8,777
Has anyone got these to actually work?
1660157694698.png


I got given 3 to fit today. I normally use AICO but have often wondered about these ones.
Mains powered, plenty of space inside, all looking good.
Instructions say to press learn button on each device, turn mains on, and fit detectors.
All was going according to script at this point.

Then I tested them.
-Kitchen also sounded Top of stairs but not Bottom of Stairs.
-Bottom of stairs also sounded Top of stairs and Kitchen (correct result)
-Top of Stairs also sounded Bottom of stairs but not kitchen.

So I "Unlearned" them (press button 9 times) and start again.
Same result.
Phoned support who said to learn them again, their final words being "good luck", and they were basically just reading from same manual as me.
At this rate the only place they are going is back to the wholesaler. Unless there are any tips or tricks anyone knows!

(There are plenty of YouTube videos which AFAIK apply to a different product range and have a different learning procedure)
 
Unless there are any tips or tricks anyone knows!
I think you answered your own question with
I normally use AICO but have often wondered about these ones.
And you should have kept wondering about Fireangel products
At this rate the only place they are going is back to the wholesaler.
The best place for them IMO they are a waste of time

At one of the shows I visited in the last 12 months the guy on the Fireangel stand had a sales spiel of "We can do everything that the Aico kit does for around 10% less" my response was that is a matter of opinion
 
Thanks guys. The lack of a swarm of replies saying "read the manual" or "they always work for me" tells me what I needed to know.
This job was working with an old time mate who's a builder, and I foolishly let him buy some of the materials. Never again!
 
Still have problems in-house with 12 detectors it’s such a pain to learn & unlearn… how is it possible to set them up …Again….in situ… I can’t see the amber light…. Nightmare 😎
 
Last edited:

Reply to FireAngel RF-BW-T RF Ceiling bases in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I'm having a full house rewire. I want to have mains smoke alarms, heat alarms, carbon alarm next to boiler, internet connectivity to notify...
Replies
36
Views
6K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
890
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Not come across this before, so would like some help, please. I went to install smokes and heat alarm (to new Scottish regs) in a fairly modern...
Replies
2
Views
1K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock