Flex used in domestic install

Discuss Flex used in domestic install in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
3
Hi I have been asked to carry out a second fix on a house another spark wired and now hasn't time to do. When looking at the job I noticed he had used 1.5 t&e from the consumer unit to the first smoke detector then looped around in 4 core flex. Them same was doe on the 2 way Switching extractor fans and room stats. I personally use 3 core and earth. What is people's views on this?
 
It's pretty clear in the Regs that it is permissible. That's not to say that many wouldn't consider it poor practice though, and given that it's more expensive to do it this way it's hard to see what is gained. I bet he hadn't intended ferruling the ends either.
 

Reply to Flex used in domestic install in the UK Electrical Forum area at ElectriciansForums.net