Hi guys, Im having a blonde moment. Im on a re-wire at the mo and the customer wants 2 way lighting for hall way and landing lights both ways. So will I need 2 3-core and earth cables between the switches? So basically its one light switch to do downstairs and then one to two way upstairs, then the same again but for upstairs. Does anyone have a wiring diagram I could see, sorry its been a long day.
 
Guess you haven't got your OSG with you. Oh well, live feed to sw1 com, sw1 L1 to sw2 L2, sw1 L2 to sw2 L1. Sw2 com to ceiling rose. Make sure you identify the strappers.
 
if you mean you want to switch either area from up or downstairs [2gang 2way] take the brown and blue from the fitting to terminals 1and2 the black and grey[of the 3 core] into the same connections the brown into the common repeat for the other switch dont forget to put brown sleeve on cables.
 
Last edited by a moderator:
Rite so I've wired two 3 core and earth cables to each light switch, and a twin and earth to each fitting. Is this right to avoid the dreaded borrowed neutral?
 
Sounds ok to me. T+e from sw1 to c/rose 1 and connect N in the switch with a wago, same in sw2 to c/rose 2 and job done. The 3 core plus cpc are the strappers, N and cpc so no shared N and its the same length as L, easier to test.
 

Reply to Hallway and landing wiring in the Australia area at ElectriciansForums.net

Similar Threads

Suggestions / solutions please anyone? I have a 2 way switch, Hall and Landing, power being fed on Landing. When the switch is turned on, the...
Replies
2
Views
551
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
738
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
933
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
630
Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
744

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock