- Reaction score
- 17,165
so what goes to 3 and 4 in the hive
The Hive replaces the programmer.
Terminal 3 is DHW on and terminal 4 is CH on.
Discuss help with unvented cylinder, cobi with dual channel hive in the Central Heating Systems area at ElectriciansForums.net
so what goes to 3 and 4 in the hive
As I have already said
The feed from the switchfuse goes to the boiler, only the boiler, nothing else.
Terminal 2 from the boiler is the 230V feed out to the external controls. Terminal 2 supplies power to the external controls.
Terminal 1 at the boiler is the switch live in.
There is more than one way of connecting this system but the following will work.
Run 3 core flex from switchfuse to boiler.
Connect the brown to L, the blue to N and the earth to earth.
Do not connect anything else to the supply from the switchfuse.
Using the 5 core flex you have already run from boiler to terminal box.
Connect blue to N and earth to earth at both ends.
Connect brown to boiler terminal 2 and the live supply of the controls terminal box.
Sleeve the black with brown sleeving at both ends, connect it to terminal 1 at the boiler and the boiler switched live at the controls terminal box.
Make the grey safe at both ends.
this is last post im sick now, this has to be correct?The Hive replaces the programmer.
Terminal 3 is DHW on and terminal 4 is CH on.
No you have terminal 2 on the boiler linked to terminal 1 in the wiring centre which is unnecessarythis is last post im sick now, this has to be correct?
No you have terminal 2 on the boiler linked to terminal 1 in the wiring centre which is unnecessary
finishedThe Hive replaces the programmer.
Terminal 3 is DHW on and terminal 4 is CH on.
that 1 has to be correct nowYes it is, otherwise the wiring centre won't have a permanent live for the valves.
so if i just double up the zone valves 1 and 2 it will be ok, as im only using 1 zone, plumber must of just got the kit like this and left it like it is, or does it need changingYes it is, otherwise the wiring centre won't have a permanent live for the valves.
Given that the diagram still shows the live feed from the spur to terminal 1 of the wiring centre it isn't neededYes it is, otherwise the wiring centre won't have a permanent live for the valves.
Given that the diagram still shows the live feed from the spur to terminal 1 of the wiring centre it isn't needed
In fact the boiler may be fed from terminals 1 & 2 in the wiring centre as in the diagram posted at #26 by the OP
Reply to help with unvented cylinder, cobi with dual channel hive in the Central Heating Systems area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.