Hob to socket distance - thoughts?

Discuss Hob to socket distance - thoughts? in the UK Electrical Forum area at ElectriciansForums.net

Sibo14

-
Reaction score
3
74D05C0A-2F4E-4CA0-ADC7-59B96E961177.jpeg
 
That looks very close.. Well within the 300mm and not far up from the hob.
Whats the situation?
 
A local NHBC inspector for new builds in my area will allow 300mm sockets away from sinks and drainers and 100mm minimum from a heat source (hob) be it gas or electric.
As Murdoch says there’s no minimum distance stated in bs 7671 only that accessories should be suitable for the environment and proximity
I’ve read various industry guidance which gives a distance of 100mm from a heat source ,will most likely satisfy bs 7671.
If this is a new install then I’d say that socket is too close for my liking and common sense/judgement must be used.
 
Last edited:
Distances from hobs will most likely fall into the realm of manufacturers instructions and what your local building inspector will allow.
As I said earlier the site I sometimes go on, the building inspector will allow a minimum of 100mm from the hob so I don’t think any pdf out there makes that much difference really.
 
Whoops rest of my message went- so it’s a new build flat my girlfriends mate has bought. I was asked to do the snagging on it.
This is obviously too close from a common sense standpoint but I couldn’t find a reg to back it up. Should I push to get It moved for her..? The sparky mob are NIC and it’s generally pretty poor work throughout
 
Whoops rest of my message went- so it’s a new build flat my girlfriends mate has bought. I was asked to do the snagging on it.
This is obviously too close from a common sense standpoint but I couldn’t find a reg to back it up. Should I push to get It moved for her..? The sparky mob are NIC and it’s generally pretty poor work throughout
Can’t believe the NHBC inspector passed it as safe as on my site he’d flag it a red item
 
The OSG gives guidance on such distances for your 'evidence'. As its a new build seems a bit poor. Wasn't one of the first built, where someone got their measurements wrong? :)

They could just remove the socket and replace it with a blanking plate.
 

Reply to Hob to socket distance - thoughts? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock