That looks very close.. Well within the 300mm and not far up from the hob.
Whats the situation?
 
Do they use the socket while using the cooker?
 
A local NHBC inspector for new builds in my area will allow 300mm sockets away from sinks and drainers and 100mm minimum from a heat source (hob) be it gas or electric.
As Murdoch says there’s no minimum distance stated in bs 7671 only that accessories should be suitable for the environment and proximity
I’ve read various industry guidance which gives a distance of 100mm from a heat source ,will most likely satisfy bs 7671.
If this is a new install then I’d say that socket is too close for my liking and common sense/judgement must be used.
 
Last edited:
Distances from hobs will most likely fall into the realm of manufacturers instructions and what your local building inspector will allow.
As I said earlier the site I sometimes go on, the building inspector will allow a minimum of 100mm from the hob so I don’t think any pdf out there makes that much difference really.
 

Reply to Hob to socket distance - thoughts? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
808
hi looking to install a new induction hob to current wiring . the wiring i have is thick white probably about 15mm wide and is hard wired into...
Replies
0
Views
879
  • Question
I am PAT testing an induction hob. It passes the Earth test, but then fails on the Insulation Test. Item is about 3 years old, no damage to unit...
Replies
2
Views
409
Hi, searched the forum but cant locate anything similar so apologies if ive missed something. Ive got a new hob to install in the kitchen...
Replies
5
Views
1K
I'm either going mad or blind, but I went looking in the brown book the other day to find the small bit where it gives minimum support spacings...
Replies
5
Views
324

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock