Search the forum,

Discuss How do you test Earth Bonding? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

1

1337

How do you test the earth bonding to the water or gas pipes / what tests need to be done?
Should you connect to the pipe itself of the terminal on the pipe?
 
How do you test the earth bonding to the water or gas pipes / what tests need to be done?
Should you connect to the pipe itself of the terminal on the pipe?

Ask yourself this...
Exactly what are you trying to achieve by doing the test and why are you doing the test (its not because it says in a book, there is a reason behind it)???
How can you do what you need to do?????
 
Set to Ohms, test on earth cable in consumer unit and connect other end to pipe? So just an R2 test?

What about if the lead won't reach from DB to pipe??
Does it matter if the resistance of the leads is included in the result???
What about possible parallel paths, could they influence the result???
What is an acceptable reading?????
What are ther easons behind us doing the test????
 
Its not an R2 test as its an earth bond not a cpc, its classed as wander lead method. Earthing and bonding are not the same thing 1337.
 
Ok, very good answers..

What do we need to do before we disconnect conductor at 1 end to remove parallel paths, and why do we need to do it?

Why do you think we are given a low guidance figure of 0.05 ohms as a maximum value, what are we trying to achieve with this main protective bonding conductor?
 
Last edited by a moderator:
to achieve touch voltage of less than 50V

Although why would you disconnect the bonding to remove parallel paths? Parallel paths would be present under fault conditions.

You would remove the bonding to test ZE though.
 
to achieve touch voltage of less than 50V

Although why would you disconnect the bonding to remove parallel paths? Parallel paths would be present under fault conditions.

You would remove the bonding to test ZE though.

To test the continuity of it, how do you know you've tested it if you've included parallel paths in your test? :smile5:
 

Reply to How do you test Earth Bonding? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock