Discuss How to work out TIC!!! in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

P

PvNewbie

Hi

Given that...

Total Installed Capacity (TIC) is the maximum capacity at which an Eligible Installation could be operated for a sustained period without causing damage to it (assuming the Eligible Low-carbon Energy Source was available to it without interruption), a declaration of which is submitted as part of the processes of ROO-FIT Accreditation and MCS certified Registration.

Then how do I work out TIC? Is it the KWp of panels times the published inverter efficiency? (e.g 97%)

Thanks

Newb
 
The maximum capacity of a PV system is limited by the maximum output from the inverter. So you may need to take more than just the raw efficiency figure into account.

Also inverters typically have efficiencies that vary depending on the level of input voltage. Most quoted single figures are the maximum possible at a particular spot on the curve - which may not be the spot that gets hit by a particular panel configuration.
 

Reply to How to work out TIC!!! in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
I presently do domestic gas, plumbing and electrical work. I have worked out that 85% of my work is not electrical any more, and what I have been...
Replies
41
Views
5K
I have an elderly client that wants some additional sockets adding to a ring final circuit, some are simple spurs and some will need the ring...
Replies
35
Views
4K
L
I'm NAPIT registered FULL SCOPE which states - and is therefore approved to undertake the design, construction, maintenance, verification and/or...
Replies
45
Views
6K
E
If you want to save on your monthly electric bill and reduce your greenhouse gas emissions at the same time, you might buy a new, energy-efficient...
Replies
0
Views
986
Electricity News --
E

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock