Where the client says it is only a little job....

When you get there, there is no main bonding, no RCD, no spare ways in the CU (usually a 3036 4 way board) and/or no CPC on the lighting circuit, and they want class I (from B&Q)lights fitting, and on it goes...

The upshot of this is a bloke down the pub does it anyway, lol
 
If you fit a 3.2kw cooker on the ring without 30ma rcd protection i think your a fool. Why ? whats so dangerous about a cooker ?


Dont forget this is a TT system. Yes , and it has a upfront 100mA rcd , so what ?

a kettle is not fixed equipment and there is no comparison to be made between a kettle that is on for 3 minutes and a cooker that maybe on for three or four hours possibly a lot longer That true , no arguement there , but youre talking about the de-rating of a ring mains capacity , has no connection the issue of rcds.

............................
 
Nothings dangerous with the cooker especially apart from the fact that its made from metal and if fault occurs its only a 30ma rcd or lower that protects life.

socket outlet circuits on a TT system must be protected by a residual current device with an operating current of 30 mA and as he wants to spur off the existing it needs rcd protection.

I dont want to argue im just saying that i would not fit this cooker without a 30ma RCD regardless of what obsure regulation you can find.i would also fit it on its own radial. i might be going over the top in your eyes but at least when i leave i know its safe
 
Ex Army,

Welcome to my world,

Where the client says it is only a little job....

When you get there, there is no main bonding, no RCD, no spare ways in the CU (usually a 3036 4 way board) and/or no CPC on the lighting circuit, and they want class I (from B&Q)lights fitting, and on it goes...

The upshot of this is a bloke down the pub does it anyway, lol

yep, i really can't be bothered with this one either. i'm back there at 9 in the morning, still havent decided what to do. i said this evening i'll have to RCD protect anything i fit which would mean changing the board, so i said i'd have to carry out an EICR first before i could price for the work, which is going to be ALOT as the board is the opposite side of the house to the stop cock and the gas meter and theres no bonding. and the house is a tip, and dirty.
 
the board is the opposite side of the house to the stop cock and the gas meter and theres no bonding. and the house is a tip, and dirty.
Didn't know you'd been round here, should have stayed for a brew... :)
 
No bonding ??
lol , then youre not going to be doing any work till that sorted.
if i was you i'd just price mself out of the job , sounds a whole load of hassle unless the customer is gonna pay for all the extras.
 
so if i was to fit a new board, i'd have to fit a 100mA time delayed RDC main switch? also i would fit bonding, and what about the main earth to the erath spike? it's 10mm at the minute, dissapears into the wall and i can't see where it goes. how do i go about fettling this upto the 17th edition, and how do I test it?
 
No bonding ??
lol , then youre not going to be doing any work till that sorted.
if i was you i'd just price mself out of the job , sounds a whole load of hassle unless the customer is gonna pay for all the extras.

Have you weighed the client up yet? Judging a book by it's cover is never good (and sometimes it goes wrong) but is there money in it for you? Are they likely to go for it OR are could this be a factor as to how they ended up with a shoddy job done in the first place?

If in doubt price yourself out of it and walk away:thumbsup
 
No bonding ??
lol , then youre not going to be doing any work till that sorted.
if i was you i'd just price mself out of the job , sounds a whole load of hassle unless the customer is gonna pay for all the extras.

yeah thats looking like the option i'm leaning towards, i'll do the EICR and then whack in a sky high price...
 
so if i was to fit a new board, i'd have to fit a 100mA time delayed RDC main switch? also i would fit bonding, and what about the main earth to the erath spike? it's 10mm at the minute, dissapears into the wall and i can't see where it goes. how do i go about fettling this upto the 17th edition, and how do I test it?

No need to fit a 100mA TD upfront, provided the CU you replace it with is Class II (plastic) and at least a Dual RCD split load, see OSG p16 Fig 2.1(iii).
 
Have you weighed the client up yet? Judging a book by it's cover is never good (and sometimes it goes wrong) but is there money in it for you? Are they likely to go for it OR are could this be a factor as to how they ended up with a shoddy job done in the first place?

If in doubt price yourself out of it and walk away:thumbsup

yes, the person paying for the work is the landlord, who owns several properties, and the people who bodged the cooker have worked on his houses for years and never had any problems before (nothing short of a miracle from some of the wiring i saw today) i'll get some pics on my periodic tomorrow
 
so if i was to fit a new board, i'd have to fit a 100mA time delayed RDC main switch? Yes

also i would fit bonding, Yes
and what about the main earth to the erath spike? it's 10mm at the minute, Needs to be 16mm
dissapears into the wall and i can't see where it goes. You need to find and check the rods condition , but it sounds like its giving good readings from your earlier posts.

how do i go about fettling this upto the 17th edition, and how do I test it? Use earth loop test from CU main switch terminals and earth rod conductor.

.........................
 
so if i was to fit a new board, i'd have to fit a 100mA time delayed RDC main switch? Yes

I disagree, if fitting a new board then all circuits will be protected with 30mA protection so the 100mA could be binned and an isolator fitted in it's position or tails sent straight into the board.
 
Why does he have to fit a 100mA TD upfront RCD Biff ?, if he replaces the CU with a plastic Dual RCD one there is no reg that says you must fit an additional Upfront TD 100mA RCD.

I Know some sparks have their own preference on this, as I would consider it in certain circumstances, but on such a small domestic install I wouldn't bother.

Likewise on the earthing conductor, so long as the cable isn't buried he could use 6mm, in fact if it was mechanically protected it is possible to use 2.5mm on a domestic TT (not that you would).
 
And just as i thought we might be getting near the end of this long journey lol.

Hey it's only stating I disagree ;) I'm not trying to start an argument over it lol

Perhaps I have typed before engaging brain but I do not come across many TT installations so perhaps you know something I do not? If so I would be more than happy for someone to enlighten me and I will stand correct. We've got 6 minutes for me to learn something new today:thumbsup

Make that 5 :D
 
Why does he have to fit a 100mA TD upfront RCD Biff ?, if he replaces the CU with a plastic Dual RCD one there is no reg that says you must fit an additional Upfront TD 100mA RCD.

I Know some sparks have their own preference on this, as I would consider it in certain circumstances, but on such a small domestic install I wouldn't bother.

Likewise on the earthing conductor, so long as the cable isn't buried he could use 6mm, in fact if it was mechanically protected it is possible to use 2.5mm on a domestic TT (not that you would).

I stand corrected with the point of not needing 100mA if dual 30mA ( im blaming it on the liquor lol )
However if he cant prove the rod earth conductor is mechanically protected when buried ( and i bet its not ) then 16mm is required.
 
But youre right , i'd be happy to use the 10mm if its giving good readings , i cant be arsed digging up the drive for a new rod install either
 
i said this evening i'll have to RCD protect anything i fit which would mean changing the board,


Stand alone Rcd
It will certainly make you more competitive than John from the Pub,that's comparing to the proposed all singing and dancing 17th compliant and possibly un necessary new board
 

Reply to in after a cowboy, cooker nearly burnt the house down! in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock