- Reaction score
- 38
Out of 28 circuits in main house only getting current flow on 2 and they are small 0.1 and 0.5 amps. Yet when I check flow from main DB on L3 it was 4.6 amps. Done IR and Continuity and all fine.
Discuss Investigation on massive electricity bills in the UK Electrical Forum area at ElectriciansForums.net
I'm glad you even understood his/her comment. I do hope s/he isn't an electrician!Do you think that £4100 is acceptable for a quarter when they know they don't use a lot of electricity themselves. Clearly they don't want free electricity and I can assure you they quite well off but why would anyone pay for something that they are not using regardless of how much money they have. Really don't see the point in your comment.
are they producing &selling bob hope, you need to gain access in the cottage and see what is going on !
Is their any thing leaving from their board going out has a sub!
Hi - well if 30A went in and 6A came out, there is 24A dripping away in between ... I would turn all circuits off that the house DB and see what's going down their sub main. An IR test of the sub main to the house perhaps?Nothing!!!!! All very strange. Can't seem to find a problem anywhere apart from the fact that L1 spikes but only reading 6 amps at the other end.
27184/180/24 = 6.5 kW continuous =6500/230=28 A continuous on a single phase. Having read all the posts, I would be very suspicious of the meter. Also I would put a clamp ammeter around the incoming 3 phase plus neutral cable and check that the current balance is zero (or very near zero). Many early 3 core XPLE cables with combined N&E armouring have been found to rust through leaving any out of balance N current (which you will have here) to find its way back via the other (ground) paths. That can interfere with the 3-phase meter accuracy. I and the DNOs/RECs have found this at many sites - at one commercial site I once found 330 A entirely returning via earthed building steel and metal water and gas pipes and not along the cable as it should have been. Everything was working fine at that site - I was there to investigate wobbling VDU computer displays - caused by elevated 50 Hz magnetic fields due to the currents in the structural steelwork. I am not saying the above will be the answer - but certainly worth checking for.Meter readings all seem to coincide. Found out it's an actual meter reading every 6 months so every other quarter is an estimate based on last reading. Just checked the last two actual readings and in the 6 months usage was 28187 KWh. Think it's at 13p so that would work out at £3664. Please correct me if I'm wrong. Any other ideas welcome.
and one of thosenow either the thermal imaging camera
Well the couple in the cottage have just got back and now the supply to the cottage is pulling anywhere between 10 and 37 amps sometimes sitting at a steady 17 but also sits at around 26. Something going on there. More detective work needed.
The only type of device where the current increases when the voltage is reduced (constant power) is one that is powered through Switch Mode Power Supply. I am an ex-designer of Switch Mode Power supplies.Is the supply to the cottage undersized? If there's significant volt drop between DB and cottage then, V=IR, if volts go down amps must go up.
To cut a long story short the voltage was about 2 milliamps finding it’s way through my clients house back to the supply, but the clamp meter does not care aboutvoltage just amps.
Do you mean millivolts?
Yes, My mistake.To cut a long story short the voltage was about 2 milliamps finding it’s way through my clients house back to the supply, but the clamp meter does not care aboutvoltage just amps.
Do you mean millivolts?
Is the supply to the cottage undersized? If there's significant volt drop between DB and cottage then, V=IR, if volts go down amps must go up.
Not necessarily true. Over the range of voltage at which they will operate correctly, some loads, mostly SMPSUs, have negative dynamic resistance, because they consume approximately constant power regardless of voltage. Current is therefore approximately inversely proportional to voltage. However, outside of the operational range, the current usually falls to zero as the device shuts down. There are other loads that behave like constant power loads integrated over a longer period of time, mainly thermostatically controlled heating. Increasing the voltage drop of a heating circuit, such that the heat dissipated by the cable causing the drop doesn't heat the target space, will require the heater to be on for a greater duty cycle to maintain the set temperature as its heat output will have decreased. But the consumption at the meter won't have decreased by the same amount, so the energy consumption to maintain the temperature will increase by the amount lost through voltage drop.
On the job now. Reading a constant 7.6 amps in L3 incoming on main board. This L3 also had a constant 4.8 amps to main house. Any ideas
Just been in and the only circuit pulling any significant current is the cooker at 6.6 amps. Don't know why it kept spiking but it's only since they got home. L1 was pretty much inactive until try arrived then starts spiking at 36 amps at times.
Reply to Investigation on massive electricity bills in the UK Electrical Forum area at ElectriciansForums.net