Search the forum,

Discuss Is this "surrounded by insulation or on 100mm insulation in your opinion? in the UK Electrical Forum area at ElectriciansForums.net

I guess you mean Pp 177 on brown on site guide. Just to expand on balanced load viz RFC, I guess the most load would be the kitchen sockets at around 25% of the way around the ring circuit. This is a studio flat with 50 m² floor space. So washing machine, toaster, kettle etc. would be at that point. So you are saying (and I have seen it reference often that the load will mostly (or all?) go onto the run to the kitchen? and the long leg of the ring will take hardly any load. Is there any scientific basis for this or regs. Can't say I have seen any. I just wonder what science this is based on. If that is the case it defeats the whole reason for having a ring then? Might as well do radials (4mm)
Just to beat this to death, the asterisk on the methods points out the cable must be touching the plasterboard in order to conform to the ccc tabulated. I am not positive it will actually contact it very well.
 
I guess you mean Pp 177 on brown on site guide.
That has the typical CCC for different methods. It is also present on page 84 as Table 7.1(iii) following the "standard circuits" that I was looking at.

Page 75 has the various RFC combinations of OCPD and cable size that seem to be considered "standard". If you look at the table then only 4mm is listed as acceptable for methods 101 or 103. Previously it was the longer length that I looked at when considering 4mm (e.g. 171m instead of 106m on VD limit).

Just to expand on balanced load viz RFC, I guess the most load would be the kitchen sockets at around 25% of the way around the ring circuit. This is a studio flat with 50 m² floor space. So washing machine, toaster, kettle etc. would be at that point. So you are saying (and I have seen it reference often that the load will mostly (or all?) go onto the run to the kitchen? and the long leg of the ring will take hardly any load. Is there any scientific basis for this or regs. Can't say I have seen any. I just wonder what science this is based on. If that is the case it defeats the whole reason for having a ring then? Might as well do radials (4mm)
With method 103 a 4mm radial is only going to be good for 17.5A so with socket outlets then 16A MCB.

You probably would need two 4mm radials for the kitchen if you have more than two ~3kW loads (e.g. washing machine and dish washer perhaps?) as they would really have to be on separate radials, and at that point you might as well do the whole flat as a RFC in 4mm! More so if AFDD are needed...

Also if doing 4mm radials it is no different to a RFC for wiring. Provided you avoid spurs as then most sockets (all in RFC) have only 2 * 4mm cables. Which you should, as they are the Devil's work.

Just to beat this to death, the asterisk on the methods points out the cable must be touching the plasterboard in order to conform to the ccc tabulated. I am not positive it will actually contact it very well.
There are various ways you might look to getting out of using 4mm cable. Going to LSZH version rated at 90C gets you something like a 22% increase in CCC and the accessories are OK as your use of CSA and working current is the same as for 70C PVC, just you are relying on hotter safe running in the thermally insulated region.

Dropping the RFC to 20A is another route to keeping a limit on possible cable heating, but you might find it is getting close to probably total load if the kitchen has a good few gadgets.

But all of those might just bite you if there is any trouble down the line. Sticking to the OSG combinations from Table 7.1(ii) (for RFC, lights, or radials) is by far the easiest route to having a safe and justifiable design for most domestic work!
 
Last edited:
I guess the most load would be the kitchen sockets at around 25% of the way around the ring circuit. This is a studio flat with 50 m² floor space.
With 4mm VD is really not an issue, you could deliberately make one leg take a longer route so the heavy loads are closer to half-way. They need not be exactly there but if you are looking at, say, 75m of cable in total, then running the short leg an extra, say 20m back, is not going to be an issue.
 
You've probably considered this already, but where the cables run through the insulation, running them in flexible conduit brings you to ref A. This will allow most of the standard circuits in standard sizes, eg 32A/6mm cooker, 32A/2.5mm ring etc.

Surprised that a 4mm ring can be run ref 103. They are very flexible circuits those rings.
 
You've probably considered this already, but where the cables run through the insulation, running them in flexible conduit brings you to ref A. This will allow most of the standard circuits in standard sizes, eg 32A/6mm cooker, 32A/2.5mm ring etc.
Trouble is you would have to run each T&E in its own conduit or you are penalised by the grouping factor.

I'm not sure the effort of puting in conduit is going to make up for any savings in copper cost or termination effort in going 4mm!
Surprised that a 4mm ring can be run ref 103. They are very flexible circuits those rings.
Indeed, a very good solution for a typical flat/floor.
 

Reply to Is this "surrounded by insulation or on 100mm insulation in your opinion? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock