Discuss Just curious (earthing) in the UK Electrical Forum area at ElectriciansForums.net

littlespark

-
Esteemed
Arms
Supporter
Patron
Reaction score
17,020
I’m not working on this… not yet anyway, but can someone tell me why there’s a fuse or a link on the earth here?

IMG_5127.jpeg


The green wire is bonded to the metal mainswitch and the installation is metal conduit.

I don’t know if the bare wire is an incoming earth off the cable, going out to a rod or linked to the lightning conductors.

It was just having a removable cut out like this which means very easy to disconnect and leave something not earthed/bonded.
It’s not even sealed.

Or is it just a type of connection block I’ve not seen before
 
It could just have a link in it and been used as a connector - I wouldn't worry too much about the chances of disconnection as it's no different to a proper MET bar with a removable link. However it's an odd setup as it's presenting as TNS but claims by the label on the head (and the CNE link terminal on the side) to be PME!
 
I thought it was just a head with a link, rather than a fuse. Just strange that it can be so easy to pull it out.
Different if it was a lid which needed to be removed to access the connector screws like any other Henley type 100A block.

I’ll have a good look next time I’m there…
 

Reply to Just curious (earthing) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
536
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
394
I've wired some cable to a small 3x3 shed with 2 gpos, a 15a GPO, and a light. The shed is about 2m away from the house on a concrete slab. The...
Replies
0
Views
541
Hi all Done a EICR on a flat which had the link fuse in the service head .. had an earth wire coming off the orange cable to an earth block...
Replies
16
Views
818

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock