I have the walls open (removing tiles from dot and dab walls fml...)

Can i connect a single FCU 13a to both my integrated Fridge Freezer and Microwave? or would i need to have two seperate FCUs for this? or would i need a 20a DP Switch? wiring inplace is part of the ring main.

Microwave is 1kw max and Fridge Freezer im trying to find out as i cant seem to find it online... (beko bcfd350)

I dont mind for maintenance if one needs servicing both get switched off. I have seen forums where it seems its just personal preference to run separate so would be great to know the regs of it.

I am just trying to downsize the number of sockets we have in the kitchen as it was cluttered with 7 fcus within a 3 meter distance!


Thanks!
 
The regs only stipulate that a FUSED connection unit can supply any number of points, whereas an UNFUSED connection (ie double pole switch) can only supply one point. “One point” can mean a double socket however.

We call them fused or unfused spurs off the rfc.

So, yes you can have one fused or unfused switch supplying a double socket with a fridge freezer and a microwave.

A lot of kitchens now have a bank of module built grid switches, with double pole switches in it… can have up to 4 switches, usually engraved with the appliance name, taking up a regular 2 gang box.

Looks neat, but an absolute chore to work on with 6 x 2.5 cables. (2 from the rfc and 4 outgoing)
 
Looks neat, but an absolute chore to work on with 6 x 2.5 cables.

and a pain in the arse when the 20a? switches burn out when carrying only 50% of their rating.
 
I remember when kitchens were designed for a purpose rather than what the sockets looked like. Will it really make a big difference to your life to have one less FCU on your kitchen wall?
 
Looks neat, but an absolute chore to work on with 6 x 2.5 cables.
The regs only stipulate that a FUSED connection unit can supply any number of points, whereas an UNFUSED connection (ie double pole switch) can only supply one point. “One point” can mean a double socket however.

We call them fused or unfused spurs off the rfc.

So, yes you can have one fused or unfused switch supplying a double socket with a fridge freezer and a microwave.

A lot of kitchens now have a bank of module built grid switches, with double pole switches in it… can have up to 4 switches, usually engraved with the appliance name, taking up a regular 2 gang box.

Looks neat, but an absolute chore to work on with 6 x 2.5 cables. (2 from the rfc and 4 outgoing)
yes i have seen that but arent they 20a rated? is that fine to be on the ring?

i did see that last night actually i was thinking a double grid by Schneider lisse with the marked labels

GGBL02GBSB - Plate​

GGBL20DPMWW - example switch marked with microwave
 
You could use a FCU to feed two hidden sockets for the appliances, but obviously the combined load has to be under 13A and it also makes a fault/maintenance period on one a problem for both.

The grid switches are neat but some folks have seen reliability issues and you do need a deep back box and patience to wire them up as it can be cramped. They should be 20A rated but I would only put a single 13A fused load on each.
 

Reply to Kitchen Appliances Single FCU to Multiple Appliances in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock