UK Landlord Trying to Deduct Deposit for Unnecessary Electrician Test.

Discuss Landlord Trying to Deduct Deposit for Unnecessary Electrician Test. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi everyone,

I recently moved out of my rented property, and as expected, my landlord is attempting to withhold a significant portion of my deposit. One of the charges she's insisting on is £300 for an electrician to conduct an EICR test.

Here's the situation: I'm a qualified electrician, and during my tenancy, I simply swapped the upstairs bedroom light with the living room light. I didn't tamper with any wiring; I only changed an accessory. My understanding is that no certificate is required for this kind of minor change, as there were no alterations to the wiring.

I've tried explaining this to my landlord, but she's adamant about the charge. Now, I've escalated the issue and filed a dispute with TDS (Tenancy Deposit Scheme). However, I'm hoping to get some additional confirmation and possibly a reference to the regulations that support my stance.

Can anyone confirm if I'm correct in my understanding? And perhaps provide a specific part of the regulations that backs up my argument?

Thank you in advance for any advice or insights you can offer!
 
There is no legal requirement to have an EICR completed upon a change of tenancy/occupation, but there are some recommendations to do so.
As per my post above, I think this is a point worthy of debate.

As we all know, BS7671 isn't a statutory instrument, so therefore any and all of it can be considered 'advisory' - as such, the advice (GN3) is upon change of tenancy. However - we are also informed by EAWR89 that BS7671 is considered ACOP to be adhered to. It therefore follows that EAWR89 - which is obviously statute - implies a requirement to inspect as per 652.x and GN3..... which leads us back to change of tenancy. The 2020 Act simply adds another layer of protection by adding in the five year rule over the top and more importantly does also specify "..is inspected and tested...before the tenancy commences in relation to a new specified tenancy.."

Directly from the Act: ( The Electrical Safety Standards in the Private Rented Sector (England) Regulations 2020 - https://www.legislation.gov.uk/uksi/2020/312/regulation/3/made )
Duties of private landlords in relation to electrical installations

3.—(1) A private landlord(1) who grants or intends to grant a specified tenancy must—
a)ensure that the electrical safety standards are met during any period when the residential premises(2) are occupied under a specified tenancy;​

(b)ensure every electrical installation in the residential premises is inspected and tested at regular intervals by a qualified person; and​

(c)ensure the first inspection and testing is carried out—​

(i)before the tenancy commences in relation to a new specified tenancy; or​

(ii)by 1st April 2021 in relation to an existing specified tenancy.​

(2) For the purposes of sub-paragraph (1)(b) “at regular intervals” means—

(a)at intervals of no more than 5 years; or​

(b)where the most recent report under sub-paragraph (3)(a) requires such inspection and testing to be at intervals of less than 5 years, at the intervals specified in that report.​
 
As per my post above, I think this is a point worthy of debate.

As we all know, BS7671 isn't a statutory instrument, so therefore any and all of it can be considered 'advisory' - as such, the advice (GN3) is upon change of tenancy. However - we are also informed by EAWR89 that BS7671 is considered ACOP to be adhered to. It therefore follows that EAWR89 - which is obviously statute - implies a requirement to inspect as per 652.x and GN3..... which leads us back to change of tenancy. The 2020 Act simply adds another layer of protection by adding in the five year rule over the top and more importantly does also specify "..is inspected and tested...before the tenancy commences in relation to a new specified tenancy.."

Directly from the Act: ( The Electrical Safety Standards in the Private Rented Sector (England) Regulations 2020 - https://www.legislation.gov.uk/uksi/2020/312/regulation/3/made )
Duties of private landlords in relation to electrical installations

3.—(1) A private landlord(1) who grants or intends to grant a specified tenancy must—
a)ensure that the electrical safety standards are met during any period when the residential premises(2) are occupied under a specified tenancy;​

(b)ensure every electrical installation in the residential premises is inspected and tested at regular intervals by a qualified person; and​

(c)ensure the first inspection and testing is carried out—​

(i)before the tenancy commences in relation to a new specified tenancy; or​

(ii)by 1st April 2021 in relation to an existing specified tenancy.​

(2) For the purposes of sub-paragraph (1)(b) “at regular intervals” means—

(a)at intervals of no more than 5 years; or​

(b)where the most recent report under sub-paragraph (3)(a) requires such inspection and testing to be at intervals of less than 5 years, at the intervals specified in that report.​

You should note, the "New tenancy" only refers to the FIRST tenancy (3.1c above)

Basically upon the introduction of the law:

3.1ci says the first inspection must be carried out before the tenancy (if not already a tenant)
3.1cii says the first inspection must be carried out before 1st April 2021 (if a tenant already)

From the law:

"(c)ensure the FIRST inspection and testing is carried out—


(i)before the tenancy commences in relation to a new specified tenancy; or

(ii)by 1st April 2021 in relation to an existing specified tenancy."



There is no legal requirement for an EICR upon subsequent changes of tenancy/occupancy.


Also check out 652.1 in GN3 it states that the recommendations in table 3.2 are merely recommendations and are NOT legal requirements.

It may make sense, but neither BS7671, nor GN3, nor "The Electrical Safety Standards in the Private Rented Sector (England) Regulations 2020" do not mandate an EICR upon a new tenancy (Other than for the FIRST tenancy)
 
Last edited:
You should note, the "New tenancy" only refers to the FIRST tenancy (3.1c above)

Basically upon the introduction of the law:

3.1ci says the first inspection must be carried out before the tenancy (if not already a tenant)
3.1cii says the first inspection must be carried out before 1st April 2021 (if a tenant already)

From the law:





There is no legal requirement for an EICR upon subsequent changes of tenancy/occupancy.


Also check out 652.1 in GN3 it states that the recommendations in table 3.2 are merely recommendations and are NOT legal requirements.

It may make sense, but neither BS7671, nor GN3, nor "The Electrical Safety Standards in the Private Rented Sector (England) Regulations 2020" do not mandate an EICR upon a new tenancy (Other than for the FIRST tenancy)
We may have to agree to disagree on this. The reference to a first inspection is simply to acknowledge that others may follow afterwards (at the five year or less period) for any new [continuing] tenancy.
 
You should of swapped the lights back before you moved out TBH then no-one would of known and you say you are qualified so no big task
To be honest, I wish I had thought of it. We've never rented before, so didn't think it would be a problem. I thought I was doing them a favour, as you typically wouldn't have that kind of light fitting in a living room.

I've disputed the fees with TDS now, so I will provide TDS with a minor works test certificate. I'm still disputing other fees as they're trying to charge us £120 for gardening (cutting the grass). It wasn't the season to cut the grass, and it wasn't cut when we moved in anyway lol
 
We've never rented before, so didn't think it would be a problem.

The first thing you do when you move in to a rented property should be to take detailed, time stamped, pictures of everything. Check through the inventory and check in report thoroughly and make sure any inaccuracies are fixed.

Then at the end of the tenancy return the property exactly as it was when you moved in. They will take every possible opportunity to deduct money from your deposit for even the most trivial things.

Arrange for the check out inspection to happen on the last day of the tenancy so that they can't stop you from being present for it.

When I left the first house I rented they made a deduction from my deposit to repair a damaged door frame. The door frame had been damaged by the landlord's contractor who replaced the cooker when it broke and like an idiot I told the landlord about it but didn't take any pictures. So when I contested the deduction from my deposit the landlord said they had repaired the damage caused by their contractor (they hadn't) and the damage they were charging for was other damage caused by me.

It wasn't the season to cut the grass, and it wasn't cut when we moved in anyway lol

Unless you can prove absolutely and irrefutably that the grass is exactly the length it was when you moved in then you'll probably lose that one. And even then your tenancy agreement probably states that you must cut the grass at the end of the tenancy.
 
They are obviously trying to scam you and will probably get away with it, so, as you are an electrician create some faults that only a magician could find that will show up on the EICR they are about to have done. You could then charge them £300 for info on how to fix it.
 
The rent deposit schemes are very "Pro" tenant . And tend to always believe a tenant more than a landlord . With smart phones been almost a common item there is not excuse not to be able to form a perfect paper trail for any issues. Based on the Damaged door frame mentioned... I would demand screen shots that are time/date coded to show landlords communication with the trade person , the invoice and prove of payment . And the deposit scheme should want the same ?/
 

Reply to Landlord Trying to Deduct Deposit for Unnecessary Electrician Test. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock