LED dimmer problem. Head scratching.

Discuss LED dimmer problem. Head scratching. in the UK Electrical Forum area at ElectriciansForums.net

0

067256

Hi there,
Just installed 8 GU10 down lighters each having a 4w Philips dimmable LED lamp. Installed a Varilight V-PRO 2 gang touch control LED dimmer (min load 10w) (trailing edge)
All was working great until yesterday. Been again to look and cant seem to figure out what is wrong.
1 gang does 4 spots....these work great.
2 gang does the other 4 spots but when turned on the lamps initially flicker, dim up and down, then switch off completley???
Faulty dimmer?
Cant think what else it could be?
 
Doesn't sound like it's a good match for the load you're trying to control. These dimmers will remember their previous settings. If you've dimmed that second gang less than 10/16th output you'll be below the minimum output for the dimmer.
 

Reply to LED dimmer problem. Head scratching. in the UK Electrical Forum area at ElectriciansForums.net