Thanks for your responses. Yes I can either install a pull cord or a switch outside, but the point of my post is to challenge the general assumption that you can never have a switch in a bathroom.

My response to the points raised:

  • I’m confused by the comment that IPx5 isn’t enough to protect against condensation even outside of zones. Even within zones 1 and 2 the legal minimum is IPx4. What’s the minimum you’d recommend for any other accessories in a bathroom then? IPx6? IPx7?
  • The regs state that you can have a normal 240v plug socket can be installed 3m from the boundary of zone 1. My switch would be more than 3m from zone 1, so if condensation is a problem then why can I legally install a regular socket?
I appreciate I’m in the lions’ den here but just wanted to get your views on it
Your confusion is completely justified. Like many other objectively minded reasonable people you naturally wonder why an electrician considers it fine for you to step into a shower tray and operate an electric shower while water is flowing around your feet but consider it deadly dangerous to operate a light switch 2 mts from the wet area.
 
Your confusion is completely justified. Like many other objectively minded reasonable people you naturally wonder why an electrician considers it fine for you to step into a shower tray and operate an electric shower while water is flowing around your feet but consider it deadly dangerous to operate a light switch 2 mts from the wet area.

An electric shower is designed to be used in a wet environment. It is specifically built for this purpose. A standard light switch is not, and shouldn't be operated by someone who is dripping wet.
 
An electric shower is designed to be used in a wet environment. It is specifically built for this purpose. A standard light switch is not, and shouldn't be operated by someone who is dripping wet.
A standard light switch is used in virtually every other country in the world in situations I described above. And guess what, people like you and me use them freely when we travel abroad. Ever had any problems?
 
A standard light switch is used in virtually every other country in the world in situations I described above. And guess what, people like you and me use them freely when we travel abroad. Ever had any problems?

A lot of other countries have light fittings that aren't suitable for bathrooms too. So are you also saying we should just fit whatever light fittings we want in bathrooms?

No, I've never personally had a problem. However that doesn't make it OK.
 
A lot of other countries have light fittings that aren't suitable for bathrooms too. So are you also saying we should just fit whatever light fittings we want in bathrooms?

No, I've never personally had a problem. However that doesn't make it OK.
Well let's just stick with the light switch for now.The OP made a completely reasonable comment using good sense. He is told that in the UK and here (ROI) that he is somehow in "mortal danger" if he uses a light switch in his bathroom. He has likely noticed when he goes abroad that people use switches (and sockets) in bathrooms. In fact he has done the same himself (and survived!) He has noticed that people are not lying dead in the streets.He has rightly concluded that something is not stacking up here.
 
Well let's just stick with the light switch for now.The OP made a completely reasonable comment using good sense. He is told that in the UK and here (ROI) that he is somehow in "mortal danger" if he uses a light switch in his bathroom. He has likely noticed when he goes abroad that people use switches (and sockets) in bathrooms. In fact he has done the same himself (and survived!) He has noticed that people are not lying dead in the streets.He has rightly concluded that something is not stacking up here.

Well I personally would not operate a standard light switch when I was wet from getting out of the bath.
 
Neither would I. Amazing how the continentals have managed to educate their populations in the safe use of electrics in wet areas. Could we learn something there?

Well most people in the uk probably wouldn't use the switches when wet either. But surely better safe than sorry?
 
Well most people in the uk probably wouldn't use the switches when wet either. But surely better safe than sorry?
I don't know about you but I feel comepletely safe using a light switch in a bathroom. Just like using sockets in kitchens when cooking or washing we all take common sense precautions. Now when I step into an electric shower even though as you say its "designed" I am always aware of the greater potential for danger. Having worked on them for many years (perhaps like yourself) I am not overly impressed with the "design" of them.
 
Couldn’t sleep to night, ended up pursuing on here. From my research, it seems the French for example have similar zones in bathrooms, much as we have. But apparently larger bathrooms than we. So is it a bit of a myth that they put light switches next to a bath or shower cubic?

If you consider safety, you don't see many sockets & light switches in swimming pool confines, so why would a bathroom be any less different?

Some French comments on the subject;

https://ckenb.blogspot.com/2010/06/french-light-switches.html
https://sarlwiseman.com/blog/post/french-electrical-regulations---part-2-bathroom-zones
https://www.completefrance.com/living-in-france/french-plumbing-and-electrics-1-1518579

Of course you could take it to another level.

https://www.amusingplanet.com/2016/08/denki-buro-electric-baths-of-japan.html

Must try and get some sleep now.
 
Next to the shower, no. But in zone 2 yes. Particularly common in countries like Spain, Italy etc and I believe Mike Johnson confirmed also in France.

I don't know where the practise for installing light switches outside bathrooms, ever came from. BS 7671 only ever said at worst, that said switch should not be accessible from the bath, or always outside zone 2 in recent editions.

If you read the link about zones or volumes in France I set out in my post 45, it suggests class 1 light switches can be installed in 'no volumes', the same as our guidance of installing outside of zone 2. In fact its the same distance >0.6m from the edge of the bath.

Perhaps its diy'ers in France not following the guidance. The first link to a blog, talks about light switches in France being installed outside the room its for, including bathrooms.

As a lot of UK bathrooms have a quite small floor area, sometimes the only way to achieve the guidance, is a pull cord or switch outside, unless you live in BP and have a bathroom the size squash court.

Time for bed soon :)
 
Last edited:
I don't know where the practise for installing light switches outside bathrooms, ever came from. BS 7671 only ever said at worst, that said switch should not be accessible from the bath, or always outside zone 2 in recent editions.

If you read the link about zones or volumes in France I set out in my post 45, it suggests class 1 light switches can be installed in 'no volumes', the same as our guidance of installing outside of zone 2. In fact its the same distance >0.6m from the edge of the bath.

Perhaps its diy'ers in France not following the guidance. The first link to a blog, talks about light switches in France being installed outside the room its for, including bathrooms.

As a lot of UK bathrooms have a quite small floor area, sometimes the only way to achieve the guidance, is a pull cord or switch outside, unless you live in BP and have a bathroom the size squash court.

Time for bed soon :)
Your point about DIY, ers may well be valid. From the links you posted I get the impression that the idea of zones in bathrooms is a relatively new developement for the French. But it's clear that they will allow a light switch to be installed in 0.7 meters from wet area
 
I understand your reasoning on the condensation thing. TBH all rooms have different temperature variables so condensation may not be a problem, another room with poor ventilation may suffer badly from it.

My method of thinking was water vapour condensing on a cold spot within an accessory over a period of time and not drying out, unlikely but could happen in extreme circumstances.
Obvious question in response to this ...
Why is a pull-cord switch, mounted on the ceiling where the most humid air goes, immune to this while a switch located lower down where the humidity is lower isn't ? Not only that, but a ceiling mounted switch has a higher chance of having an opening to the attic and it's cold, damp air.
 
Obvious question in response to this ...
Why is a pull-cord switch, mounted on the ceiling where the most humid air goes, immune to this while a switch located lower down where the humidity is lower isn't ? Not only that, but a ceiling mounted switch has a higher chance of having an opening to the attic and it's cold, damp air.
Spot on.
 
Obvious question in response to this ...
Why is a pull-cord switch, mounted on the ceiling where the most humid air goes, immune to this while a switch located lower down where the humidity is lower isn't ? Not only that, but a ceiling mounted switch has a higher chance of having an opening to the attic and it's cold, damp air.
I would happily use a pull cord in a room so damp the walls were dripping and i couldn't see through the mist to the other side.

touch a wet faced switch plate, hmm not with my finger, probably with an insulated screwdriver.
 
Your point about DIY, ers may well be valid. From the links you posted I get the impression that the idea of zones in bathrooms is a relatively new developement for the French. But it's clear that they will allow a light switch to be installed in 0.7 meters from wet area
Seems we were following EU regs like most other EU countries. Perhaps they were lagging behind, where we were at the forefront. From my 'plastic bath' I can't reach the light switch. Are you suggesting we should don't need to concern ourselves with that, and throw caution to the wind?
 
Obvious question in response to this ...
Why is a pull-cord switch, mounted on the ceiling where the most humid air goes, immune to this while a switch located lower down where the humidity is lower isn't ? Not only that, but a ceiling mounted switch has a higher chance of having an opening to the attic and it's cold, damp air.
Think your missing the point there. That piece of yucky string is not potentially put me in contact with electricity, but a normal plate switch might, whilst I'm sat in my bath.
 
Seems we were following EU regs like most other EU countries. Perhaps they were lagging behind, where we were at the forefront. From my 'plastic bath' I can't reach the light switch. Are you suggesting we should don't need to concern ourselves with that, and throw caution to the wind?
My friend. I
Think your missing the point there. That piece of yucky string is not potentially put me in contact with electricity, but a normal plate switch might, whilst I'm sat in my bath.
Far from throwing caution to the wind I simply suggested that if continentals can educate their kids to use common sense and instruct their kids how to safely use electrical accessories and to not "operate the light switch in the bathroom with wet hands". Do you think something similar is achievable in the UK?
 
I still can't believe people think it's a good thing to have a conventional light switch in a bathroom.
My friend. I

Far from throwing caution to the wind I simply suggested that if continentals can educate their kids to use common sense and instruct their kids how to safely use electrical accessories and to not "operate the light switch in the bathroom with wet hands". Do you think something similar is achievable in the UK?

A lot of things are achievable, but it doesn't mean they are sensible. Keeping standard rocker switches out of steamy bathrooms is a sensible precaution though.

I really don't understand why you keep labouring the point.
 
I still can't believe people think it's a good thing to have a conventional light switch in a bathroom.


A lot of things are achievable, but it doesn't mean they are sensible. Keeping standard rocker switches out of steamy bathrooms is a sensible precaution though.

I really don't understand why you keep labouring the point.
I thought I was involved in a discussion. No bother. We, ll leave it at that.
 
Seems we were following EU regs like most other EU countries. Perhaps they were lagging behind, where we were at the forefront. From my 'plastic bath' I can't reach the light switch. Are you suggesting we should don't need to concern ourselves with that, and throw caution to the wind?

Pull switches in bathrooms pre-date EU regulations. No idea who is following who, but it doesn't seem unreasonable to err on the side of caution.
 

Reply to Light Switches in Bathrooms in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net