why not swap the back box for a dual outlet box and fit 2 x SFCUs.
No wonder 'ring in mind' jumped out at me.....why not. it's rated for it? and if you have "proper" voltage of 240V, it's 15A. beaRING IN MIND THAT IT'S INTERMITTENT AS THE STAT. SWITCHES OFF WHEN THE SET TEMP. HAS BEEN ACHIEVED.and the bloody caps lock right next to the "A". stupid layout. should have been put by the Q or the Z.
What else is on the ring?32amp ring
Supplying two Spurs
What else is on the ring?
Good luck with your search please keep us informed.Afternoon all,
As title suggests I’m not sure if such a product exists but I’m looking for a 20amp contactor that is mounted into a single box/patress
Reason being another sparks has wired 2 ufh mats 1800w each onto a single spur (14-16amp)
Or solder tags.If you do end up needing one a relay will be a lot quieter than a clunky contactor. These are compact and good quality, with screw mounting lugs.