Dean Smith

I don't know if any of you have found this before. During a test today I was finding the Zs on the circuits higher than expected, I tested the loop on both sides of the main switch (new MK dual RCD board) and there was a 0.5 ohms difference!! I have had this before on an RCD and replaced the unit but wouldn't have thought a DP Switch would have this problem. If you have what did you do to rectify?
 
Have i read this correctly. you have done a Ze at the switch in the off position as you would, then done the same with it in the on position at the load side, and you have 0.5 ohm difference in your measured results. I can only assume some sort of crap on the switch tips, maybe from manufacture, have you tried operating the switch a few times to see if this improves things, if that doesnt work, then turn something on in the installation, and switch the load, the current across the tips may be enough to clean it, Just an idea.

Cheers..............Howard
 

Reply to Main Switch reducing Ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello mates. i have an MK CU to replace. As you may know, the main switch in MKs is on the left hand side. There's no way to replace the...
Replies
13
Views
1K
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
1K
OLDBOY
O
I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Replies
13
Views
375
I was called in a block of office saying they have a problem with the main incomer. During the night nit all nights randomly the main switch in...
Replies
3
Views
746
I've just picked one of these up on a famous auction site. The voltages, low and high resistance ranges all appear to be working fine but it's not...
Replies
7
Views
303

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock