Currently reading:
Maximum length of Main Bonding

Discuss Maximum length of Main Bonding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

C

claret73

I did find the answer pretty much to this in an old thread & was answered by Chris...

But wonder if I could get a few more suggestions as to being correct.
Installed a Main Water Bond from a DB Board to the Main Incoming water supply which was (in my opinion) well over 25m away. We ran it along the existing SWA supplying the Workshop/Garage. It was run in 10mm.

No Test was carried out to confirm the 0.05 Max reading and from what I can figure am not sure if the cable has a high enough CSA.

In OSG I see an R2 reading on 10mm at 20deg of 0.00183 (even though the cable is run outside for most of its length), again from Chris's answer I can only have 27m before 0.05 resistance is breached.

I'm right in saying anything over 27m needs to step up to 16mm.

If the resistance is above the 0.05 does this have no barring consequences as to the potential difference between exposed & extraneous parts? Can't seem to find the exact clarification on this.
Cheers
 
The wording is "it is recommended that the resistance of the bonding conductors does not exceed 0.05ohms. 16mm will give you a 47mtr run


Chris
 
Guys I've seen this 0.05 ohms max in various threads on here but I've not seen it in the BRB or onsite guide. Not saying it isnt there but I would be grateful if someone can point me at the reg cos I appear to have missed that one.
 
Calum what about safety circuits that have no RCD protection or Sub Mains or older installations that didn't require RCD protection?? Where would the Earth Fault Loop Path? why would you want it to be under 0.05 ohms?

I know the answers and its not "stupid"
 
From table 9A on the OSG (page 166) we get the value of resistance per metre of a given conductor cross sectional area (csa), for example:
What is the maximum permissible length of a 10mm2 protective conductor so that it is effective?
From the OSG we see that the value of resistance per metre of 10mm2 protective conductor is 1.83mΩ/metre, so the maximum length will be:
0.05 x 1000 ÷ 1.83 = 27.32 metres
Or:
L = R (max permissible resistance) x (csa) ÷ ρ (resistivity of copper = 0.0178 μΩmetre) (use 0.0183)
L = 0.05Ω x 10mm2 ÷ 0.0183 = 27.32 metres
This value is the maximum permissible length for a 10mm2 protective conductor
Cross sectional area Maximum permissible length
1 mm2
2.76 metres
1.5 mm2
4.13 metres
2.5 mm2
6.74 metres
4 mm2
10.84 metres
6 mm2
16.23 metres
10 mm2
27.32 metres
16 mm2
43.47 metres
25 mm2
68.77 metres
35 mm2
95.41 metres

This test is to ensure that the main bonding conductors are unbroken, and have a resistance low enough to ensure that, in the event of a fault, all exposed and extraneous parts will be live at the same potential.
To achieve this is recommended that the resistance of the bonding conductor DO NOT exceed 0.05 Ohms.
The reading has to be less than 0.05 Ohms to be acceptable.
If the resistance is more than 0.05 Ohms the bonding is unsatisfactory and given a CODE 2
 
From table 9A on the OSG (page 166) we get the value of resistance per metre of a given conductor cross sectional area (csa), for example:
What is the maximum permissible length of a 10mm2 protective conductor so that it is effective?
From the OSG we see that the value of resistance per metre of 10mm2 protective conductor is 1.83mΩ/metre, so the maximum length will be:
0.05 x 1000 ÷ 1.83 = 27.32 metres
Or:
L = R (max permissible resistance) x (csa) ÷ ρ (resistivity of copper = 0.0178 μΩmetre) (use 0.0183)
L = 0.05Ω x 10mm2 ÷ 0.0183 = 27.32 metres
This value is the maximum permissible length for a 10mm2 protective conductor
Cross sectional area Maximum permissible length
1 mm2
2.76 metres
1.5 mm2
4.13 metres
2.5 mm2
6.74 metres
4 mm2
10.84 metres
6 mm2
16.23 metres
10 mm2
27.32 metres
16 mm2
43.47 metres
25 mm2
68.77 metres
35 mm2
95.41 metres

CONTINUITY TEST OF MAIN EQUIPOTENTIAL BONDING CONDUCTORS
This test is to ensure that the main bonding conductors are unbroken, and have a resistance low enough to ensure that, in the event of a fault, all exposed and extraneous parts will be live at the same potential.
To achieve this is recommended that the resistance of the bonding conductor DO NOT exceed 0.05 Ohms.
The reading has to be less than 0.05 Ohms to be acceptable.
If the resistance is more than 0.05 Ohms the bonding is unsatisfactory and given a CODE 2
 

Reply to Maximum length of Main Bonding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock