Search the forum,

Discuss MCB then RCD in the Commercial Electrical Advice area at ElectriciansForums.net

peeko

-
Reaction score
10
Hi everyone, hope you can help

Recently we've completed an EICR on a commercial property and it's thrown up some issues with the lighting. The installation method is rough as, T&E just chucked on top of the ceiling tiles as we've all seen a million times before so we'll be sorting this as part of the remedial works.

One of the issues I have is that I'm not convinced from looking at the state of it is that the cables in the walls/partitions of the office areas have the adequate 50mm protection/are inside metal conduit, therefore as per amendment 3 I've got to provide RCD protection to the circuit.

The circuits come off an old Square D 3 phase DB, and if anyone has had the misfortune to look for RCBO's that fit these, they'll tell you they're hard to get hold of and cost a small fortune. My idea is this - adequately protected cable from the current MCB to a separate enclosure of double pole RCD's, which then provide protection to each lighting circuit.

I've been told this is OK, just wondered if anybody has experience of this, pro's/con's etc? Obviously in an ideal world I'd swap the board for something more modern with RCBO's that are available/not a fortune, but for a couple of circuits I don't think they'd go with the cost of this, maybe down the line as they make alterations.

Thanks in advance
Charlie
 
Sounds like a plan to me, people often do this in domestic for new shower circuits etc.

Only thing I'd say about it is make it bloody obvious that there's a protection device after the MCB - if somebody on site needs to reset it, they may not know it's related if it's not obvious to them.

P.S. Isn't this a bit above the remit of a PAT Tester? ;)
 
:p very much above the remit of a PAT tester!

Won't be attempting myself - our sparks will be installing/testing/cert-ing, just like to make sure they're not bull****ing me at times, especially when it's a scenario I've not seen before.

Installation is about 35-40 yrs old
 
Hi Andy, they sent me 2 part codes - however every site I check says they're discontinued, not keen on putting used in off fleabay
 
"One of the issues I have is that I'm not convinced from looking at the state of it is that the cables in the walls/partitions of the office areas have the adequate 50mm protection/are inside metal conduit, therefore as per amendment 3 I've got to provide RCD protection to the circuit"


Has the client requested the code 3 work?
 
Hi Andy, they sent me 2 part codes - however every site I check says they're discontinued, not keen on putting used in off fleabay

I would persist with that one. Last schneider rcbos I used in a square d tpn board was only a couple of years ago.
 
Thanks Andy, I'll have another look, might be a case of ringing round to see if anyone has any surplus stock gathering dust

You could even ask about on here. Start a thread and see if any members have any kicking about, like you say, gathering dust. Not sure what part of the forum you would be best putting in though.

Jay
 
Schneider rcbos are readily available for Square D KQ boards. I am not so sure, if it is a QOE board that they are compatible but I could be wrong.
 
I've just recently fitted Schneider KQE RCbo Devices In a square d push fit bus bar 3 phase Board. Funny really about five years ago I sold a load of square d rcbos becaue couldn't see me using them and already go ample stock of MCB and rcbo devices. My wholesaler holds them for me. Some say ironic at what the Schneider cost in region of 50-60 quid.
 

Reply to MCB then RCD in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
610
As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
691
Morning guys, I would like some advice, currently at my workplace, I am replacing a DB and existing wiring in a warehouse. One of the ways feeds...
Replies
4
Views
1K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
989
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
465

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock