Hi all , Simple question for you all, current job has MCCB panelboards fitted with adjustable trips which allow the tripping characteristics to be altered to 40% of maxim full load current. Manafacturers data sheet has max Zs values , but only for the origanal current rating of the unit ie 400A ,250A etc.

The client has done a protection study and has tweaked the breakers to suit his needs , Obviously now they are not set at maximum so how do i find the Max Zs for each device now?? Would the manafacturers be of any help or is it a case of performing some calculations to establish them ?

ANy pointers welcomed as normall work on HRC fuse panels which obviuosly have a set value of Zs .



Cheers

Nick
 
Use the Max Zs given by the manufacturer. As these are adjustable, there is nothing stopping anyone from adjusting the setting to x1. ....If the max Zs is good for the rated maximum current of the MCCB, then it's good for the lower setting selected.


You always use the ''Max Zs'' as stipulated on the manufacturers data sheet, with any adjustable type MCCB...
 

Reply to MCCB Max Zs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi everyone, Happy Friday! Could someone please point me in the right direction, I’m after the Max Zs for a Bill Talisman TLF633 63A MCCB, I’ve...
Replies
4
Views
1K
Hi everyone, Happy Friday! Could someone please point me in the right direction, I’m after the Max Zs for a Bill Talisman TLF633 63A MCCB, I’ve...
Replies
0
Views
899
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Heeelp! I have an 11kW/21A motor which is attached to a hydraulic power pack. I have replaced the old panels with new, using the same star delta...
Replies
17
Views
2K
BEFORE I pull my hair out looking over a gazillion google results..... wondered if anyone here has come across a device that will do something...
Replies
1
Views
876

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock