I don’t know if it was mentioned earlier, but is this a moulded on plug, or one that’s been put on?

It may be that the connections inside the plug are loose, rather than the wall socket.
Its a moulded plug on the dryer.The actual dryer plug didnt get hot it was plugged into an extension cable.It was the feed into the extension plug ,the plug and socket ,that got very very hot.That was why I asked if the dryer itself can disrupt voltage flow somehow.Excuse non tech terms.just an unqualified bod trying to work it out.The extension cable itself is a mega tough bit of kit.Not from b and q.?
 
Its a moulded plug on the dryer.The actual dryer plug didnt get hot it was plugged into an extension cable.It was the feed into the extension plug ,the plug and socket ,that got very very hot.That was why I asked if the dryer itself can disrupt voltage flow somehow.Excuse non tech terms.just an unqualified bod trying to work it out.The extension cable itself is a mega tough bit of kit.Not from b and q.?
Two possibilities
1) The extension cable is not adequately rated (despite its claims!) - or maybe faulty. It does look the part, but can't really see the csa of the conductors.
2) There is a fault with the dryer, though if there was, you might expect the dryer plug itself to also be getting hot (eg if the fuse was warming up), but you say it was OK.
 
Last edited:
Two possibilities
1) The extension cable is not adequately rated (despite its claims!) - or maybe faulty. It does look the part, but can't really see the csa of the conductors.
2) There is a fault with the dryer, though if there was, you might expect the dryer plug itself to also be getting hot (eg if the fuse was warming up), but you say it was OK.
You are right to consider all possibilities. Maybe the heating up this time was unconnected with the original issue.All will be revealed tomorrow.A sparky will come galloping over the hill with assorted tech stuff and will sort it out.It was terrifyingly swift and potentially deadly whatever happened.Left unattended it would have been a house fire.
 
Left unattended it would have been a house fire.
There I would disagree with you, I don't believe there would. To get their product approvals to be sold legitimately, the materials of both the plug, and the socket on the wall, will have passed a glow-wire test to demonstrate they won't support combustion. So although there may be loads of melted plastic and a horrible smell, there shouldn't be flames to create a house fire.
 
There I would disagree with you, I don't believe there would. To get their product approvals to be sold legitimately, the materials of both the plug, and the socket on the wall, will have passed a glow-wire test to demonstrate they won't support combustion. So although there may be loads of melted plastic and a horrible smell, there shouldn't be flames to create a house fire.
unless there's flammable material/s close to the socket.
 
It's possible but unlikely that the dryer is taking too much current. If it did, because it would be producing proportionately more heat, the most likely symptom would be that the dryer overheated, not the plug. And it has various thermal cutouts and limit stats to prevent that happening.
 

Reply to Melted Plug and Socket cause in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
642
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
1K
Hi all I need some advice and thoughts on what caused this plug on a toastie maker to have given me electrical shock when I pulled it out of the...
Replies
6
Views
1K
Hi, This post is about my concerns with medical IT socket outlets and want to alert you all if you are fitting them in a hospital. The current...
Replies
20
Views
2K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
888

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock