Melted socket

Discuss Melted socket in the UK Electrical Forum area at ElectriciansForums.net

Jhcp1977

DIY
Reaction score
11
Hi can simeone give me advice I had a electricia install a outside socket that has melted the plug before I ring him can someone tell me if it's been installed correctly? I can't find the makes anywhere online are they inferior products?
I am not happy as my daughter was in the hot tub at the time so shouldn't have something tripped in the house or the RCD on the lazyspa ? As with it all being melted it was still working it's only because she could smell burning I was alerted to it ?
So from what I can see the middle switch is what it's connected to with a single cable running to a outside weatherproof socket any help appreciated
 

Attachments

  • PXL_20210428_073307083.jpg
    249.8 KB · Views: 84
  • PXL_20210428_074112762.jpg
    302.8 KB · Views: 78
no danger in the tub per se. . the only danger would be the outside socket getting hotter and damaging the cable/s feeding it, and any close combustible materials catching fire. get the sparks to fit you a good quality plug while he's there.
 
Why was it open all night? that type of outside socket has a lid that can be closed once the appliance has been plugged in, did you in fact do that or was the socket left exposed whilst the spar was in use? The socket could have been splashed with water from the spar, which contain chemicals and compromised the plug.
No it was left open as I just forgot to close it after switching electric off in the house and unplugging it
 
Thank you all speaking to a different electrician I explained that's there's a single 2.5 twin and earth run straight from a outside socket to a 32amp MCB and he said that's not right any way I will wait and see but what's your opinions on that correct or not
 
Not sure but this is on it
that's a 10mA RCD factory fitted in the tun lead.
as for the 2.5mm cable from a 32A MCB, is that cable direct from the MCB or is it a spur off a socket in the house? if it's spurred off a socket on a ring final, as long as it's the only socket on the spur, it's compliant.
 
Thank you all speaking to a different electrician I explained that's there's a single 2.5 twin and earth run straight from a outside socket to a 32amp MCB and he said that's not right any way I will wait and see but what's your opinions on that correct or not
As long as that cable is supplying only the one double socket outlet, it is technically OK, as the fuses prevent an overload to the cable, though instinctively people would expect to use a 16 or 20A MCB on that circuit.

The issue you had/have is nothing to do with the fixed wiring, and everything to do with the plug and fuse within it.

The fixed installation cannot detect when something connected externally to it gets hot - it could be a toaster (which is OK getting hot), or it could be a loose connection in the plug or poor quality plug/fuse (which would be a problem).

I would suggest either the plug/fuse is not of proper quality, or a connection was loose.

Could you post additional photos of the plug, especially the pins and markings on the pin face?
 
that's a 10mA RCD factory fitted in the tun lead.
as for the 2.5mm cable from a 32A MCB, is that cable direct from the MCB or is it a spur off a socket in the house? if it's spurred off a socket on a ring final, as long as it's the only socket on the spur, it's compliant.
It's 2.5 From outside socket no spurs nothing just that one socket on its own mcb
 
Ask the electrician to fit another plug. Then ask him to measure the current when the spa is in heat mode and then measure current when in heat and bubble mode. You need to confirm that the current is no more than 2050/240 Amps and 1850/240 Amps respectively. Meanwhile I will look up spec and call company. The failure is over current and thence overheating of fuse . This plug socket combination is suitable for no more than constant 10amps because the plastic and rubber construction makes it very difficult to dissipate heat especially generated in the fuse.
 
https://images-eu.ssl-images-amazon.com/images/I/F1cu1b3il5S.pdf

see page 10. The maximum power may well be 2050 + 800 + 50 = 2850 Watts for heater, turbo and pump unless the controller switches off parts of heater when turbo turned on. You need the measurements of current drawn in all the spas modes of operation.

As before a 13Amp plug socket in plastic and rubber with lid of socket closed will fail on overheat if over 10A drawn for more than 30 minutes. The heating effect of the current is a quadratic function ie heat produced is proportional/varies as current x current or current squared. Thus heating effect at 12A is 1.44 times greater than at 10A ie 12 x 12/(10 x 10) - At 13Amps it is 1.69 more than at 10Amps. Typically the fuse and its holder will produce a few watts of heat at rated current which if it is not conducted away will cause considerable increase in material temperature and thence thermal damage as one can see from the photos.
 
Last edited:
I have submitted a technical query on line and will update once I have a response. Meanwhile I have just come off the phone with lazy spa uk support desk who confirm the maximum power consumption of your spa is 2050 Watts so about 8Amps. Time to call the sparks back to measure those currents. If they do not exceed 8Amps or thereabouts then it points to the inadequacy of or fault with the socket plug combo and/or its standard of installation. If more than 10A then I would suspect a fault with spa itself causing excessive over current and overheating as described earlier which you should report and pursue with supplier or lazy spa uk.
 
Last edited:
Studying the plug and a similar one on our kettle ( 2.5kW) in attached photos - the region of most intense heating seems to be along an axis through two points; the middle of the fuse and the rivet joint of the line terminal - upper fuse clip assembly. These two points are both high current density and thus high Joule heating. Permaplugs use bussmann fuses so of good quality. The live plug pins and socket entries show no sign of overheating. Telltale signs to ponder on.
 

Attachments

  • 18505D4F-E289-491A-AE3A-DE96A644630E.jpeg
    304.3 KB · Views: 29
  • D714396F-F199-4003-8C46-5BC62D76F419.jpeg
    302.6 KB · Views: 33
Last edited:
I reckon it would not have been much longer before carbonisation of the plastic former between the plug earth pin and top fuse clip precipitated a line earth tracking current which would be detected by the supply side rcd turning off the power.

My learned EF colleagues may wish to advise the OP on specific questions to ask and confirm with the sparks before he visits since this is an IET special location and installation (GN7 IIRC).
 
Last edited:

Reply to Melted socket in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock