Afternoon all,

Just trying to clear something up, going through regs book at present.

Basically have got a TNC-S/PME installation, 16mm tails, 60/80a main fuse (think it is 60A), 6mm bonding to water and 6mm coming from service head to block then into CU as main earth.

Am I right that being as it is PME I am obliged to upgrade bonding to 10mm as per table 54.8 and that the note about bonding must be not less than half size of CSA for main earth only applies to conditions other than PME.

Just wanted to be clear as that's how I'm reading it, the job is a mains change. Thanks in advance.
 
If you wait a couple of weeks and its got plastic incomer won't need bonding big tin hat on-off the cuff remark.

As I understand the draft, I might be wrong, the metallic pipe entering the building need not be bonded;

'Chapter 41 Protection against electric shock
Section 411 contains a number of significant changes. Some of the main ones are mentioned below.
· Metallic pipes entering the building having an insulating section at their point of entry need not be connected to the protective equipotential bonding (Regulation 411.3.1.2).'
(Hager)

Whereas before, it was a slam dunken?
 

Reply to Minimum bonding size TNC-S in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock