Discuss Selecting bonding conductor size in the UK Electrical Forum area at ElectriciansForums.net

Has anyone here seen a bonding conductor thermally damaged? It sounds odd to me.
Yes this is an often quoted statement promoted by the Best Practice Guides. Thermal damage may not necessarily be visible to the human eye so must be taken with a pinch of salt, as I say BS7671 is what you must follow.
 
You have no way of knowing. What you must do is follow BS7671 and not some random person from the NICEIC.
So we should assume all installations have been wired up wrongly? I don't think so. Everything points to this installation having been correctly done for the regs at the time. And I disagree that you should blindly follow BS7671 without referring to the Onsite Guides, Best Practice Guides, GN3 etc. Plus the NICEIC technical helpline is there for a reason and is the most qualified advice I have at hand so I'm going to follow it. Especially (I don't mind admitting it) if it saves ripping a house apart in the process.
 
So we should assume all installations have been wired up wrongly? I don't think so. Everything points to this installation having been correctly done for the regs at the time.
I actually think it's not really relevant that it may have met the regs in 1966. There weren't as many PEN faults then!

Isn't the wider principle that if you are significantly altering an installation, the right thing to do is to ensure the alteration complies with the regs today. BPG1 says this on page 5 before proceeding to give questionable advice.
At the end of the day you are putting your name to an EIC saying it complies with BS7671:2022 (unless you specifically list this as a departure of course, and then it's supposed to offer an equivalent level of protection, so I don't see how that stands up to scrutiny)

Personally, I think the "it will probably be ok" get-out-clause in BPG1 is daft and is exceptionally daft if it's PME, as the point is that with no warning a PEN fault could see the bonding carrying the entire return neutral current. There wouldn't be any signs of thermal damage if it hasn't happened before (as @Aaron b said)

Regarding "ripping a house apart", the regs do allow bonding to be "as close as practicable to the point of entry", and on a couple of occasions I've left original undersized bonding in place and added some new 10 sq mm to the nearest convenient point.
 
I actually think it's not really relevant that it may have met the regs in 1966. There weren't as many PEN faults then!

Isn't the wider principle that if you are significantly altering an installation, the right thing to do is to ensure the alteration complies with the regs today. BPG1 says this on page 5 before proceeding to give questionable advice.
At the end of the day you are putting your name to an EIC saying it complies with BS7671:2022 (unless you specifically list this as a departure of course, and then it's supposed to offer an equivalent level of protection, so I don't see how that stands up to scrutiny)

Personally, I think the "it will probably be ok" get-out-clause in BPG1 is daft and is exceptionally daft if it's PME, as the point is that with no warning a PEN fault could see the bonding carrying the entire return neutral current. There wouldn't be any signs of thermal damage if it hasn't happened before (as @Aaron b said)

Regarding "ripping a house apart", the regs do allow bonding to be "as close as practicable to the point of entry", and on a couple of occasions I've left original undersized bonding in place and added some new 10 sq mm to the nearest convenient point.
I agree somewhat that the advice that 'if a conductor hasn't suffered thermal damage then it's ok', doesn't make complete sense.
So I'm in a position where I don't quite understand the reasoning behind the guidance, but it is the quidance that I have been given by my governing body. It's not as if I just rang up some random guy and he gave me his personal opinion; he was clearly quoting the NICEIC's stance on the subject of undersized bonding cables and unequivocally advised me that the 6mm bonds need not be changed. I was given the impression that there was no reason to change the bonding cables at all if there was no sign of thermal damage. And it's not recorded as a departure as no alterations have been made yet. I have raised my eyebrows before during DIS assessments at comments made by assessors, but the technical helpline seems to be more from the horse's mouth and I'm not really in a position to doubt their advice. Certainly something worthy of further discussion though.
 
Well you had decided the NICEIC is the advise to follow before you came on here as it is the easy option and as long as you feel you are satisfying 132.16 then all well and good.
 

Reply to Selecting bonding conductor size in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
689
Hi, searched but still niggling problem need help on... Installation: - 4mm earth to earthing electrode (rod) Ra 42ohm Zdb 33ohm 1361 60A main...
Replies
19
Views
3K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
445

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock