Discuss New kitchen, live earth fault!! in the UK Electrical Forum area at ElectriciansForums.net

A N/E fault still warrants rectification before its energised, considering there has been a board change, all circuits should have been tested prior to the change and any issues included in the quote for the work, to find a fault then re-energise it after the board change is arris about face and poor work ethics from any supposed qualified competent electrician.
 
Thank very much for all your help and advice, these lads genuinely want to resolve the problem, although some critical and concerning comments, I will show them this thread, a friend kindly suggested posting on here for independent thoughts and advice.
Please keep posting more thoughts and comments.
 
Please give us any feedback, as regards my comments and to further your understanding, a N/E fault more than often won't pose an actual risk to yourself as such but there are situations where a N/E fault is definately a cause for concern, this cannot be comfirmed with just a meter reading and requires further investigation hence my concerns that it has been re-energised although I am in the party of thinking that any N/E fault should not be energised until it has been corrected regardless whether the fault was new or pre-existing.
 
Last edited:
I suspect the neutral/earth fault is existing and has nothing to do with the kitchen frolics.
Please give us any feedback, as regards my comments and to further your understanding, a N/E fault more than often won't pose an actual risk to yourself as such but there are situations where a N/E fault is definately a cause for concern, this cannot be comfirmed with just a meter reading and requires further investigation hence my concerns that it has been re-energised although I am in the party of thinking that any N/E fault should not be energised until it has been corrected regardless whether the fault was new or pre-existing.

Thanks again, and I will certainly reply to let you know the outcome.
 
Thank very much for all your help and advice, these lads genuinely want to resolve the problem, although some critical and concerning comments, I will show them this thread, a friend kindly suggested posting on here for independent thoughts and advice.
Please keep posting more thoughts and comments.

In all honesty, the lads who genuinely want to resolve this problem shouldn't of been touching electrics in the first instance.
You should pay for a registered Electrician to come out and find the issues, put them right and then you should counter charge.
 
Is it just me or is the r2 for the RFCs too low, measuring bonding or a fault or ... And the R1+R2 for the RFCs (neatly typed in the R1+R1 column ...) is too high ?

I would be interested to compare actual readings with those on the cert.

Wonder what the scope or description of works says on the first page?
 
As already said , tell them you will employ an independent electrician in if the problems not sorted , which may be a you're best bet in the long run anyway..
 
They probably did not mention the neutral to earth fault as the schdule does not have a box for N/E insulation test results.
Wonder why the shower is on a 5 sec dis ?
Type (Type )MCB s theses must be new!

On a serious note putting the up sockets on the non RCD side of the board is unaccepable and fobbing you off saying badly wired plug ,they new the fault was there when or if they tested (might of been RCD not holding test when energised) as all plugs etc should of been removed for testing!

Cash in hand or whatever method of payment the elctrician has changed the CU and has to do this as per the current regulations!

A few tests prior to the CU being changed would of identified any IR problems and I wonder if the house has a borrowed neutral what with both lighting ccts on the same RCD.

A picture of the inside of the consumer unit would be good!

I do hope this issue is resolved sooner rather than later let us know!
 
@mhar - When filling out test sheets, it asks for the max permitted value as stated by the BS7671 not the adjusted value for temp' compensation that the onsite guide gives you.
 
@mhar - When filling out test sheets, it asks for the max permitted value as stated by the BS7671 not the adjusted value for temp' compensation that the onsite guide gives you.
Hi DW and MHAR - These days I put a clarifying comment in case Inspector Clouseau wants to look. Hopefully readers are aware of the need for the 2 values. ;)
Cheeky Comment : As the OSG values seem calculated by applying BYB Appendix 14 to Table 41.3, l guess you could say it was the max value from BYB ?
 
The fact that the test results bear almost no relation to what is installed and written on the consumer unit is very suspicious.

The fact there is a neutral-earth fault on the upstairs sockets may mean that any leakage could be passing through the earth bar of the consumer unit and then passing along the bonding cable and onto the gas pipe. We don't know if the consumer unit is properly earthed do we?

I hope this gets sorted :)
 
Last edited:

Reply to New kitchen, live earth fault!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
770
Hello, Last year I had some electrical work completed in my house (New CU, SWA for garage, downlights) I informed the electrician that I will be...
Replies
8
Views
2K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
824
Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
952
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
792

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock