baazab

-
Reaction score
23
hi avery1 need your help i done new rewire and theres proplem with lighting circuit,iinsulation resistance between LN-earth IS 120 useing megger mft1533,and same problem with same circuit getting 48volts between switch wire and earth with switches off...please p;ease help me :crazy:
 
if that reading is 120Meg. then it's fine. worry not. now link out L-E at 1 end and measure R1+R2. do the same with N-E. the 48 volts could be due to a broken or poor connection on the cpc.
 
m or M??????? need to get it right. one is milli ohms, the other is Meg ohms.
 
hi avery1 need your help i done new rewire and theres proplem with lighting circuit,iinsulation resistance between LN-earth IS 120 useing megger mft1533,and same problem with same circuit getting 48volts between switch wire and earth with switches off...please p;ease help me :crazy:
listen kid...
after reading this..jack it in...go get an experienced electrician in as Mr Biff has said...
 
well if nothings tripping and the ins. res. reading is a massive 120Mohms............

then whats the problem exactly ?.............
 
hi avery1 need your help i done new rewire and theres proplem with lighting circuit,iinsulation resistance between LN-earth IS 120 useing megger mft1533,and same problem with same circuit getting 48volts between switch wire and earth with switches off...please p;ease help me :crazy:
120meg ohm?? If so then its fine your allowed 2 ... It's just people have a tendency to write +200meg ohm on the test sheet and people get led to believe that's the minimum.. I'd happily put my tongue on the insulation with that much resistance mate :)
 