hi avery1 need your help i done new rewire and theres proplem with lighting circuit,iinsulation resistance between LN-earth IS 120 useing megger mft1533,and same problem with same circuit getting 48volts between switch wire and earth with switches off...please p;ease help me :crazy:
 
if that reading is 120Meg. then it's fine. worry not. now link out L-E at 1 end and measure R1+R2. do the same with N-E. the 48 volts could be due to a broken or poor connection on the cpc.
 
m or M??????? need to get it right. one is milli ohms, the other is Meg ohms.
 
hi avery1 need your help i done new rewire and theres proplem with lighting circuit,iinsulation resistance between LN-earth IS 120 useing megger mft1533,and same problem with same circuit getting 48volts between switch wire and earth with switches off...please p;ease help me :crazy:
listen kid...
after reading this..jack it in...go get an experienced electrician in as Mr Biff has said...
 
well if nothings tripping and the ins. res. reading is a massive 120Mohms............

then whats the problem exactly ?.............
 
hi avery1 need your help i done new rewire and theres proplem with lighting circuit,iinsulation resistance between LN-earth IS 120 useing megger mft1533,and same problem with same circuit getting 48volts between switch wire and earth with switches off...please p;ease help me :crazy:
120meg ohm?? If so then its fine your allowed 2 ... It's just people have a tendency to write +200meg ohm on the test sheet and people get led to believe that's the minimum.. I'd happily put my tongue on the insulation with that much resistance mate :)
 

Reply to new lighting circuit problems in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
429
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
658
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
552
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock