Search the forum,

Discuss New supply to factory in the Electricians' Talk area at ElectriciansForums.net

Reaction score
145
Just wondering what people thoughts are on obtaining a supply to a part of a local mill where I am now a maintenance engineer. The existing installation is terrible with many switch fuses that have been added over the years, the oldest part is from 1946.

The total supply capacity in question is 1000Amps and enters a 1000A Dorman Smith main switch then off to bus bars. Lead tails are taken from these bus bars to the old 1946 busbars via a oil filled Pot breaker (stamped at 600A)

A local contractor is proposing removing the second oil filled pot breaker fitting a switch fuse, the busbars do not look big enough to be rated at 600A however they are proposing taking tri rated tails onto the output of the main breaker.

Personally I would much prefer a new switchboard to be installed and the 600A feed to the new factory be taken from there, this also allows for any emergencies if there are any issues where the feeds could be re routed to this switch board.

My concernes are with the reliability of this old switch and using the existing busbar chamber as a cable way, also the capacity of the lead cable feeds as there is no indication of what the oil filled breaker is turned down too.

The issue is I’m not sure what to propose, I’d like a new feed taken from the 1000Amp Dorman Smith to a new switchboard, is this a feasible idea? The existing load is around 400A however this will reduce once the new plant is running.

What’s everyone’s thoughts? I know it’s difficult to suggest but I just think what’s being proposed is a terrible idea, it may be functional at the start when there’s hardly any load but it will be increasing over the next 7 years. This also has to be done while the place is running as it cannot be shut down for weeks obviously. My aim would be to remove as much load from the old part as possible.

B37B8EBF-820F-4364-8C62-7ACB10C8210E.jpeg

AD9907E5-3C18-4862-A56E-F5EC6A117422.jpeg

2C8F722C-3B69-4BBE-9ADC-6B25586609A3.jpeg

ED1C3604-17BC-41DE-8E6C-9EB336916569.jpeg

BE025799-F4E1-4371-84CF-C49B80092C6F.jpeg
 
When you say lead cables do you mean PILC. So they are going to resupply the old busbar with tri-rated from the main 1000A mccb, leave the existing switch-fuse in place then take a supply from the old busbar through a new switch-fuse.
 
I am now a maintenance engineer.
The issue is I’m not sure what to propose, I’d like a new feed taken from the 1000Amp Dorman Smith to a new switchboard, is this a feasible idea? The existing load is around 400A however this will reduce once the new plant is running.
IMO, I think you are biting off more then you can chew.
 
Hi, sorry it is quite hard to describe, but ill try my best.

No, they are leaving the exiting set up alone with the old PILC singles feeding the oil filled breaker (this is fed from busbars protected by the 1000A dorman smith MCCB)

Paper wrapped Cables then come out of the oil breaker to supply the right and left hand side busbar chambers. They are installing a switch fuse in the bottom of the old busbar chamber and supplying it via tri rated through the busbar chamber to the 630A switch fuse as the busbars do not look like they are rated at 600A, i presume around 300A/side. The dash pot circiut breaker with the do not switch on sign will be removed (this is an unkown rating) and used to supply the building that was demolished for the new factory. Technically the busbars should be able to supply 600A per but im not sure of regs in 1946! and whether they go on the presumption that you would'nt load one side to the complete capacity of the breaker

I would much prefer to see a new supply taken from the main 1000A MCCB to a new switch board, where sub mains could be moved to, one by one as and when required. It would also allow a future proof
supply to the new extension.

There is a lot of un knowns with the plan as well as some non compliance issues.
 
Last edited:
IMO, I think you are biting off more then you can chew.

Totally agree but i am not and will not be undertaking the work, but i am questioning what is getting done at the moment
 
What scope of works are they working to?

If it's just for a new supply to the new factory then that's what they appear to be doing.

They wouldn't be preparing for replacement of all existing old, but probably serviceable, switchgear unless the scope suggested it.
Obviously the replacement of existing would have significant cost implications.
 
It is only for the supply of the new extension however i am questioning the way in which it is getting done as i don't think the 1940 switchgear is capable of supplying reliably 600+amps, it is already drawing 170A and the main dash pot breaker is rated at 600A this could be turned down inside, the mill estimates requiring 630A supply.

It has been known to trip occasionally as well!

The only way i see feasible is to install another switchboard and take this new supply from that, this would enable spare ways to be facilitated and which should have been highlighted when they asked for the new supply.

The fact of the matter is that the old switchgear will never be removed and nor am i suggesting this however i do question adding to it to the extent of it's full capacity at this stage in it s life, surely it is unpredictable.
 
I'd be looking at your budget allowance and time scales before making any decisions. Shutdown time is essential.
 
Money is not really an issue to be honest, shut down would be carried out a night.
The new extension is not populated with machinery and wont be for another year or so.

The worry for me is when the extension is fully kitted out with milling equipment they start getting random tripping, who knows if it will reset!
 
Money no object, look at Schneider panel boards.... but it's not going to be an overnight job. You'll need shutdown to completely remove and replace.
 

Reply to New supply to factory in the Electricians' Talk area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top