Page 337 cites UL testing, where arc resistance was found to be only 30 milliohms:


https://www.nfpa.org/assets/files/AboutTheCodes/70/70_A2022_NEC_P02_FD_PIReport_1of2_rev.pdf

(You may need to sign in to view, its free)


Anyway, here is the value and equation as dervied from UL:

1618029070382.png



The assumption was made (key word) that the minimum available fault current in a residential US panelboard would be 500 amps, and as such a breaker with a 300 amp magnetic pickup may provide parallel arc fault coverage for 50 feet or 2.08mm2 wire and 70 feet of 3.31mm2 wire.


Regarding the UK Ze is known in addition to R1+R2, so the full circuit already has parallel arc fault coverage.

Reason why I'm posting this is to further supplement my warning to the UK: AFDDs provide no more protection than existing MCBs, RCDs and plug tops fuses.

AFCIs were created for us merely to compensate for the lack of loop impedance.
 

Reply to Parallel Arc Fault Resistance Found to be 0.03 Ohms in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Derailed another thread with AFDDs, so I am starting this one. I will simply say that UK RCDs and MCBs provide arc fault protection as is. UL not...
Replies
212
Views
21K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock