Can somebody advise on this situation with the latest wiring regs and whether an RCD is required at the CU.

New PIR lights required front and back of house. There is a ring main socket at top of stairs which has space next to it for a 3amp FCU. Plan would be 1.5mm twin and earth in conduit from this FCU directly through the wall into a waterproof junction box which is above a garage. 1.0 or 0.75mm pond flex from junction to lights front and back, which are low powered 20w LEDs.

The upstairs ring main is not rcd protected. The wiring and lights outside will not be accessible unless you use a ladder and climb on the garage roof however I believe that this may still require RCD protection at the CU?

I'm guessing an RCD FCU or RCD plug into existing socket would still not comply? I'm confused thanks.
 
my take on this is that although the outside lights theemselves do not require RCD protection installed as per your ost, the RFC that you are altering should be brought up to current standards. i.e. RCD protection for the whole circuit.
 
If this is a dwelling the additional lights will need additional rcd protection. Can you show a pic of your consumer unit.
It's an old squareD CU. It's a family members not mine. There is one old RCBO protecting the kitchen sockets.
 

Attachments

  • IMG_20210815_193729_edit_18918129546071.jpg
    297.2 KB · Views: 22
That's a Qwickline board and rcbos are available but you are looking at £70 odd just second hand. The circuit breaker at circuit 4 is also broken.
 
That's a Qwickline board and rcbos are available but you are looking at £70 odd just second hand. The circuit breaker at circuit 4 is also broken.
Yeh cheers I've told him about the broken breaker as well. Im not an electrician but was happy to help him sort the lights if it was a simple job and met current requirements but obviously I'm not allowed to fit new breakers etc so I will advise him to get somebody in.

Shame as at a push I could have just stuck an RCD plug on and plugged it into current socket!
 
If you stick the lights on a plug, then the wiring regs don’t apply….

Sounds stupid, but that’s the way it is

To be honest, bearing in mind it's an outside light where it is high enough not to be reached, I would probably say it would be OK on a plug top. But as above, a consumer unit replacement should be high on the list of where they spend their savings.

Tin hat status = securely fitted
 
Is this true even for outside lighting, with regards to RCD protection?
It is a bit murky.

The BPG #4 guide has a C3 code for no RCD on sockets, but C2 if the sockets are likely to be used with outdoor equipment. However, I am pretty sure they are thinking of extensions leads, etc, being chopped by lawnmowers (a popular way to die in the past) and not out-of-reach lights.

You could always put the lights flex on a RCD plug, Though usually they have zero-volt release for outdoor tools so would need reset after any power cut.
 
But as above, a new CU is a really good idea here. Not only will you get all the niceties of RCD protection, you should also get surge protection and any spare parts for less than an arm & leg 2nd hand.
 

Reply to PIR lights and RCD question in the UK Electrical Forum area at ElectriciansForums.net