If you stick the lights on a plug, then the wiring regs don’t apply….

Sounds stupid, but that’s the way it is

To be honest, bearing in mind it's an outside light where it is high enough not to be reached, I would probably say it would be OK on a plug top. But as above, a consumer unit replacement should be high on the list of where they spend their savings.

Tin hat status = securely fitted
 
Is this true even for outside lighting, with regards to RCD protection?
It is a bit murky.

The BPG #4 guide has a C3 code for no RCD on sockets, but C2 if the sockets are likely to be used with outdoor equipment. However, I am pretty sure they are thinking of extensions leads, etc, being chopped by lawnmowers (a popular way to die in the past) and not out-of-reach lights.

You could always put the lights flex on a RCD plug, Though usually they have zero-volt release for outdoor tools so would need reset after any power cut.
 
But as above, a new CU is a really good idea here. Not only will you get all the niceties of RCD protection, you should also get surge protection and any spare parts for less than an arm & leg 2nd hand.
 
Cheers all. I will try and convince him to get a new CU. Especially with the price of one rcbo. Maybe I should start collecting RCBO's now with a view to selling them for more in the future as they become harder to get :cool:
 

Reply to PIR lights and RCD question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, Heavy industrial spark here, never do house bashing hence the question. I currently have a light switch at the front door not doing anything...
Replies
1
Views
484
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
340
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
581
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
854
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
591

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock