Hi all, Ive been asked to supply a 110V distribution board containing 1 x 40A and 2 x 32A DP circuit breakers. The company ordering the work has provided a new 12KVA CTE transformer.
Its been a while since I did anything like this so I just wanted some opinions on whether or not I am installing correctly.

I have a primary supply of 230V from a 50A DP mcb. from that I run 16.0mm armoured to a 63A DP isolator local to the transformer. I connect LN to the primary and earth to the earth lugs and centre tap.
I then connect 25.0mm armoured to the secondary and run through a local 100A DP 60898 and into the mainswitch of my distribution board containing the DP mcbs. I also take a 25.0mm earth from the centre tap to the earth bar of my distribution board. (the earth is therefore connected from supply-transformer-centre tap-110v disboard)
If memory serves me correctly I willhave 110V between my supply cables and 55V to earth.

Does this all sound OK to you guys? Aslo, do I use 2 x brown cables for the 110v supply to dis board as neither are a neutral?
Please go easy on me, its been a while since I tackled this.

Thanks.
(Apologies if this posted twice, tried a couple of times but couldnt find it)
 

Reply to Please help 110v distribution in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
817
Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K
Hi All, I have a question trying to understand earthing arrangments SO, We have a DNO Substation, 4 Core armoured Feeding the Distribution Board...
Replies
12
Views
2K
Guys in a solar PV plant room I have a single phase LV board for power and lighting. This is fed via 2 phases off a solar inverter through a 415 >...
Replies
20
Views
2K
I'm sure this will have been covered before but please bear with me. Have been asked to replace a main Distribution board for a fairly small...
Replies
23
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock