Hi all,

I’m getting confused as to what the DNO are going to be installing as there main supply and as you all may be aware they tend to be a little shy at replying back.

We have been told ukpn will be supplying us a maximum of 270kva to a block of 24 apartments.

I am assuming this will be 270 kva three phase, being 200 amps per phase (I can’t imagine it being 400 amps per phase)?
Could anyone confirm this in their past experiences?

I’m querying this as I need to know sizes for tails and isolators before they come to connect the main head.

Any help/advice be appreciated.
 

Give that a go... think 400A is what they are proposing, hopefully the head has got smaller as its a bit of a beast, lol
Thanks for reply. Would you happen to know roughly dimensions of the head. I’m hoping 600mm x 850mm (width x height) will be enough space.
 
Thanks for reply. Would you happen to know roughly dimensions of the head. I’m hoping 600mm x 850mm (width x height) will be enough space.

UKPN will have supplied you with this information, if not then you can ask for it, along with their requirements prior to connecting.

It's not just the size of the cutout itself but also the working space around it that is required.

Also note that you have been given the maximum possible KVA of the supply, what you actually get may be less than that and will possibly be what was asked for on the application.
 
Last edited:
As others have said - without sounding unkind, are you confident in your abilities with this project?
 
If you register for access to the UKPN document library online you can view a lot of their design standards and drawings for standard new supplies.

For this question you may want to have a look at
EDS 08-1103 supllies to multiple occupancy buildings
EDS 08-2100 LV customer supplies (covers supplies from standard single phase up to 1500KVA)

EDS 08-2110-08, EDS 08-2110-10, EDS 08-2110-11, EDS 08-2110-19 are drawing of various different cutout arrangements that may apply to this particular supply.
 
If you register for access to the UKPN document library online you can view a lot of their design standards and drawings for standard new supplies.

For this question you may want to have a look at
EDS 08-1103 supllies to multiple occupancy buildings
EDS 08-2100 LV customer supplies (covers supplies from standard single phase up to 1500KVA)

EDS 08-2110-08, EDS 08-2110-10, EDS 08-2110-11, EDS 08-2110-19 are drawing of various different cutout arrangements that may apply to this particular supply.
That’s great advise. Thanks a lot.
 
Bear in mind that tails for 400A are difficult to manage, even as singles, 240mm rings a bell but would have to check with the dno.
make sure there is plenty of space for the cable bends as they will be quite large, 300mm rad would not be unusual.
 

Reply to Please help DNOs KVA……?? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock