Client wants 2g socket in greenhouse, obviously IP rated,will be supplied from Rcd, the greenhouse consists of metal frame work on the ground.
Does this require MPBC
 
Client wants 2g socket in greenhouse, obviously IP rated,will be supplied from Rcd, the greenhouse consists of metal frame work on the ground.
Does this require MPBC
I would say so because the metal frame does represent an extraneous conductive part. (411.3.1.2 item v)

At least now the bonding doesn't have to be 10mm^2
 
Last edited:
Agree to disagree here, you say use the cpc of the 6.0mm for the bonding, cpc & bonding are 2 different functions.

You can use the cpc for the supply to the remote building as both a cpc for that sub board and bonding provided it meets the minimum cross section for both aspects.

You could use 2.5mm^2 for the circuit, but as it wouldn't meet the minimum for bonding, would require an additional 6mm^2 for bonding; or use a 6mm^2 combined circuit and bonding conductor.

Edit

Third choice would be a 2.5 or 4mm^2 - 3 core swa, which combined with the swa armour would give a combined x section greater than 6mm^2

Haven't got tables to hand, but pretty sure both sizes will give more than 6mm^2 combined.

Edit 2:

Even a 2 core 1.5mm^2 swa has an armour of 15mm^2 so would actually be ok for both the CPC and bonding (though I prefer 3 core for a "proper" cpc)
 
Last edited:
The key part is the second paragraph:

"Where an installation covers more than one building, a main protective bonding conductor shall be selected in accordance with the characteristic of the distribution circuit protective conductor for that particular building."



(Min 6mm^2; max needed 25mm^2 of course)
You can use the cpc for the supply to the remote building as both a cpc for that sub board and bonding provided it meets the minimum cross section for both aspects.

You could use 2.5mm^2 for the circuit, but as it wouldn't meet the minimum for bonding, would require an additional 6mm^2 for bonding; or use a 6mm^2 combined circuit and bonding conductor.
In many cases we’ve been told that supplying a remote garage from a Tncs supply a 10mm bonding must be installed if there are extraneous conductive parts in that area.
In many cases the easiest option would be to convert to a TT System & install a 6.0 mm
 
In many cases we’ve been told that supplying a remote garage from a Tncs supply a 10mm bonding must be installed if there are extraneous conductive parts in that area.
In many cases the easiest option would be to convert to a TT System & install a 6.0 mm

Why TT, just run a 1.5mm^2 swa including the armour as CPC and bonding and it meets the regs.

Cheapest option
 
I have heard of this new Reg but not perused it does it apply to all TN systems.

Yes, it basically means you don't need to size the extraneous conductive part bonding on the incoming supply, but on the supply to the particular building with a minimum of 6mm^2

The rest is the same other than a bit of clarification on what is extraneous - ie not just where a bit of metal passes through the wall!
 
I think it's poor wording though, it uses "main protective bonding conductor" to mean both the main protective bonding conductor at the incomer (which is based of the incomer size), and for the remote building.

I think "main protective bonding conductor" should be reserved for the incoming aspect and something like "remote building protective conductor " for the remote building.

Just to distinguish between them or else there will be confusion, 'when I say the main protective bonding conductor, I don't mean the main one, I mean one of the other main ones....'
 
This is what I found & only on non Pme supplies
 

Attachments

  • 70BF045C-E71C-4B58-89A0-B1C9FB309522.jpeg
    384.6 KB · Views: 28

Reply to Power point in external glasshouse in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock