I would say so because the metal frame does represent an extraneous conductive part. (411.3.1.2 item v)Client wants 2g socket in greenhouse, obviously IP rated,will be supplied from Rcd, the greenhouse consists of metal frame work on the ground.
Does this require MPBC
With that in mind that Power point will need its own earthing system ie:TTI would say so because the metal frame does represent an extraneous conductive part.
At least now the bonding doesn't have to be 10mm^2
Why?With that in mind that Power point will need its own earthing system ie:TT
What with & where from, its either MPBC or supplementaryWhy?
Just bond the metal structure.
What with & where from, its either MPBC or supplementary
Which is 10mm from a Tncs supply.Neither, the equivalent of MPBC as detailed in 544.1.1
So 6mm^2
Why, what size cable are you taking to the glass house???Which is 10mm from a Tncs supply.
Deemed as a Special location this Power Point now becomes an expensive item.
To comply it will need a TT earthing system for the greenhouse to accommodate MPBC
It‘s a 2.5mm from local ring mainWhy, what size cable are you taking to the glass house???
If you take 6mm^2 then that would meet the minimum x section.
Use the CPC of 6mm^2 as bonding for the seperate building.
Why?
Extraneous conductive partsWhy?
It‘s a 2.5mm from local ring main
The MPBC size relates to the existing earthing system isnt it
In a seperate building, therefore sized on the circuit characteristics - check 544.1.1Extraneous conductive parts
Agree to disagree here, you say use the cpc of the 6.0mm for the bonding, cpc & bonding are 2 different functions.
The key part is the second paragraph:
"Where an installation covers more than one building, a main protective bonding conductor shall be selected in accordance with the characteristic of the distribution circuit protective conductor for that particular building."
(Min 6mm^2; max needed 25mm^2 of course)
In many cases we’ve been told that supplying a remote garage from a Tncs supply a 10mm bonding must be installed if there are extraneous conductive parts in that area.You can use the cpc for the supply to the remote building as both a cpc for that sub board and bonding provided it meets the minimum cross section for both aspects.
You could use 2.5mm^2 for the circuit, but as it wouldn't meet the minimum for bonding, would require an additional 6mm^2 for bonding; or use a 6mm^2 combined circuit and bonding conductor.