Why, what size cable are you taking to the glass house???

If you take 6mm^2 then that would meet the minimum x section.

Use the CPC of 6mm^2 as bonding for the seperate building.
It‘s a 2.5mm from local ring main
The MPBC size relates to the existing earthing system isnt it
 
The key part is the second paragraph:

"Where an installation covers more than one building, a main protective bonding conductor shall be selected in accordance with the characteristic of the distribution circuit protective conductor for that particular building."



(Min 6mm^2; max needed 25mm^2 of course)
 
Agree to disagree here, you say use the cpc of the 6.0mm for the bonding, cpc & bonding are 2 different functions.

You can use the cpc for the supply to the remote building as both a cpc for that sub board and bonding provided it meets the minimum cross section for both aspects.

You could use 2.5mm^2 for the circuit, but as it wouldn't meet the minimum for bonding, would require an additional 6mm^2 for bonding; or use a 6mm^2 combined circuit and bonding conductor.

Edit

Third choice would be a 2.5 or 4mm^2 - 3 core swa, which combined with the swa armour would give a combined x section greater than 6mm^2

Haven't got tables to hand, but pretty sure both sizes will give more than 6mm^2 combined.

Edit 2:

Even a 2 core 1.5mm^2 swa has an armour of 15mm^2 so would actually be ok for both the CPC and bonding (though I prefer 3 core for a "proper" cpc)
 
Last edited:
The key part is the second paragraph:

"Where an installation covers more than one building, a main protective bonding conductor shall be selected in accordance with the characteristic of the distribution circuit protective conductor for that particular building."



(Min 6mm^2; max needed 25mm^2 of course)
You can use the cpc for the supply to the remote building as both a cpc for that sub board and bonding provided it meets the minimum cross section for both aspects.

You could use 2.5mm^2 for the circuit, but as it wouldn't meet the minimum for bonding, would require an additional 6mm^2 for bonding; or use a 6mm^2 combined circuit and bonding conductor.
In many cases we’ve been told that supplying a remote garage from a Tncs supply a 10mm bonding must be installed if there are extraneous conductive parts in that area.
In many cases the easiest option would be to convert to a TT System & install a 6.0 mm
 

Reply to Power point in external glasshouse in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
Replies
9
Views
585
Good Afternoon All, So I have a new situation to me that I cannot seem to get a definitive answer for. I trained as an electrician and did...
Replies
0
Views
810
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
843
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi all, I'm planning on adding some lighting to an old stone shed, there's currently a 2.5mm² SWA supply to the shed only supplying one IP rated...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock