Currently reading:
r1 + r2 testing

Discuss r1 + r2 testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

[ame=http://www.amazon.co.uk/gp/offer-listing/185617607X/ref=sr_1_olp_1?ie=UTF8&s=gateway&qid=1246287242&sr=8-1]Amazon.co.uk: Used and New: Practical Guide to Inspection, Testing and Certification of Electrical Installations: Conforms to 17th Edition IEE Wiring Regulations (BS 7671:2008) and Part P of Building Regulations[/ame]

hi, this link should take you to christopher Kitcher, practical guide to inspection, testing and cert. of elec. instal. its to the 16th but i found it helpful when learning how to test.

sorry link doesn't work for some reason, just search for kitcher on ebay or amazon, worth the £ imo
 
Last edited:
Hi.

If you are R1+R2 testing on a radial circuit then you simply isolate all power at the DB i.e main switch off, place a link between Line and Earth of the circuit you want to test, then go to the end of that circuit and measure the continuity between Line and Earth.

For a ring main again isolate, joint Line 1 to Earth 2, Line 2 to Earth one and measure at each socket on that ring circuit, the highest reading you get being recorded as the R1+R2 for that ring circuit.

Hope this helps.
 
Hi.

Well I would switch all other circuits off apart from the one you want to test, then go round each socket with a martindale tester to see which ones were still live, i.e on that circuit. Chances are the furthest one away from the DB will be the last. It will also have just one T+E in it.
 
Hey bud.

People just get confused at times with the letters and symbols for things (or cant be bothered to use caps lock).

Little r1 is end to end continuity on the line conductor

Little r2 is end to end continuity on the CPC.

No such thing as r1+r2

It's R1+R2.
 
the caps lock button on the computer

testing R1 then R2 is testing continuity of each conductorseperatly
R1+R2 is testing both at same time.

hehe got there before me Lenny
 
Last edited:
You know when you are at the last socket or outlet on a radial circuits as it will have the highest resitance reading and yes and single cable feeding it is a good indicator but beware as that may also be a radial off of a radial.
 
Hi.

Do you mean R1+R2 test or, the r1 and r2 tests??

pet hate of mine, but well explained my mr len :)

it can be difficult to accurately find last point in a circuit - as you move further down the circ the higher the reading , but more often than not you can guess which logical route to follow
 
I'm just bumping this thread as I have a similar question: Is there such a thing as an R2 reading? I've just been looking at one of the test sheets given out at college similar to the one that I will be using tomorrow in my Level 3 practical exam and it asks for an R2 reading as opposed to r2 (without caps). Is it just a typo, or am I missing something? Also, in the continuity part of the sheet next to it is a column for R1+R2 and a small column that says 'Ring'. I don't understand why the 'Ring' box is there; what is it asking for? There are no columns for r1, rn, or R1+RN.

Any help would be much appreciated. Thanks.
 
R2 is Test method 2 it is used to find the continuity of both earthing and bonding conductors.

In the case of Main Equipotential bonding you would disconnect the, say water bond from your MET and croc clip it, then with at the pipe you would clip the pipe, as that is my way to ensure your BS 951 clamp is secure and do your reading, using a low resistance ohmeter

In the case of what your looking at on a distribution or final circuit, you would clip a wander lead onto you CU earth bar and at each point in the circuit you would take a reading of the CPC, with your low resistance ohmeter.The highest reading would be your R2 reading which you would put into that column. If this method is done then there is no need to do the R1+R2 test, though the majority of electricians prefer this test to the R2 one

The ring box is a tick. It would be checked off if the socket outlets in the installation was wired in a ring final circuit, if the sockets were wired in a radial then it is left unchecked.
 
Thanks for taking the time to write an in-depth response, Malcolm. Reading your reply has just jogged my memory and the continuity for the ring part of the sheet makes sense again now. I knew I was missing something as it made sense last week. Thanks again.

This forum is a fantastic resource. Cheers.
 
Little r1, rn, and r2 are end to end resistance measurements, of line, neutral and earth on a ring final circuit. Cross connecting r1 and r2 then taking a measurement of these in parallel, equals Big R1 + R2.
 
Last edited by a moderator:
ok cheers, bare with me with this, on a radial circuit in a house, how would you know which is the last socket?
thanks for your help :eek:
on a radial, the last socket is the one with only 1 cable in it.
 
Little r1, rn, and r2 are end to end resistance measurements, of line, neutral and earth on a ring final circuit. Cross connecting r1 and r2 then taking a measurement of these in parallel, equals Big R1 + R2.

from what ive been shown line end to end is R1, cpc end to end is R2 and neutral end to end is Rn.
The values of R1,R2 and Rn will indicate whether or not the conductors are continuous.
Once you cross connect the conductors to create a parallel circuit thats when they become r1 r2 rn
 
What you should have been shown is line end to end is r1, cpc end to end is r2 and neutral end to end is rn.
The values of r1,r2 and rn will indicate whether or not the conductors are continuous.
Once you cross connect the conductors to create a parallel circuit that's when they become R1+R2 This is documented on the initial Inspection and Testing report
 
OP have not got a copy of the OSG? r1 r2 and rn, as well as R1+R2 is explained in some detail, as is the explanation in GN3
 

Reply to r1 + r2 testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top