Now chaps,

Will a radial circuit on a 20amp rcbo be enough to power a washing machine, dishwasher, dryer and fridge freezer?

At the moment the radial has a 2 gang to power 2 appliances and a 1 gang to power fridge freezer, possibility of spuring of this circuit to power an extra appliance?


Cheers.
 
bear in mind diversity.
1587632857482.png
not all appliances will be drawing power at the same time .
 
I wouldn’t.

Theoretically yes it would work, but good design would put a kitchen circuit as a separate ring from the rest of the house Due to the high loads On appliances.

3 of the highest loads on the property on a 2.5mm, I would say is boardering on not good design.

A 4mm radial I would be happy with.

edit: one other point I would make is I never put 2 high load appliances on one 13A double socket. From experience of many call outs they tend to burn out Over time.
 
I wouldn’t.

Theoretically yes it would work, but good design would put a kitchen circuit as a separate ring from the rest of the house Due to the high loads On appliances.

3 of the highest loads on the property on a 2.5mm, I would say is boardering on not good design.

A 4mm radial I would be happy with.
butOP might have a separate ring for the rest of the kitchen sockets and wanting the radial just for these appliances?????
 
butOP might have a separate ring for the rest of the kitchen sockets and wanting the radial just for these appliances?????
Those 3 appliances alone pretty much are the vast majority of a kitchens load on a normal kitchen ring. Putting them on a radial is lowering the current carrying capacity considerably.

Having a ring for the rest of the kitchen wont take that much load away.

i accept design and calc wise it is acceptable, but i would like to give it that bit more current carrying capacity.
 
The radial in question is in the utility, the kitchen has 2 separate radials with a total of 3 double sockets.
[automerge]1587634320[/automerge]
I'm hoping to start my extension in the next couple of years so it will all be complete new design and re wire, not that it makes any difference haha
 
Putting a fridge-freezer on a circuit with a higher than usual chance of tripping is not good, you go out for the day with something running and come back to find half your food is defrosting!

If rewiring/replacing then you could put in 4mm cable for a bigger radial, or if it is feasible add another 2.5mm run to the far end and turn it in to a ring, putting that on 32A breaker.
 

Reply to radial circuit to power washing machine, dryer and dishwasher in the Electrical Appliances Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock