Discuss Rats and tripping MCB in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
29
Can i just check something. If a rat decides to chew a cable will it trip the MCB or RCD ?

I ask because I had one house recently that had a randomly tripping MCB and it turned out to be a chewed cable. I was surprised as i would have thought it would trip the RCD but it never did. A chewed cable would cause a short not an overload.

Ive now got to visit a house thats suddenly got a tripping MCB and they've already told me they've had a rat problem recently.
 
When T+E gets nibbled, it's more likely to take out the RCD, the earth being sandwiched between the live conductors. That assumes a working RCD of course.

I guess other cable types could result in a short between L and N though, which would only take out the MCB.
 
Slightly on a tangent but I did and EICR on an old house recently and in the attic were some chewed cables where the animal managed to chew off inches and inches of insulation and in some places down to the copper exposing all 3 cores and at no point blew the fuse. While I admired the animals precison cable stripping , I had to give it a C1 for live exposed parts
 
Thanks for the responses. I'll check the appliances etc first as usual then, if that doesnt show an issue ill do an IR on the circuit. If it is a damaged cable i just hope its somewhere i can get to or bypass
 
So, an update. No continuity found on CPC, Neutral normal, Line 700 Ohms when measuring continuity. IR reading on Line 3MOhms, Neutral >2000MOhms. After quite a bit of work got IR on Line up to 600MOhms, but continuity still 700 Ohms, but both MCB and RCD now trip when only the MCB did before, so progress in a fashion! Found lots of Line insulation caught in terminals.
 
So, an update. No continuity found on CPC, Neutral normal, Line 700 Ohms when measuring continuity. IR reading on Line 3MOhms, Neutral >2000MOhms. After quite a bit of work got IR on Line up to 600MOhms, but continuity still 700 Ohms, but both MCB and RCD now trip when only the MCB did before, so progress in a fashion! Found lots of Line insulation caught in terminals.
I’m confused, when you say IR on line do you mean IR line to neutral or line to earth? 3Mohms wouldn’t be enough to trip an mcb.
 
I’m confused, when you say IR on line do you mean IR line to neutral or line to earth? 3Mohms wouldn’t be enough to trip an mcb.
Sorry, my bad, I meant these were N-L values.

Moved on considerably now. Have mapped out the faulty ring, and have isolated the section with bad cabling (and it is a bad cable) - and guess what...it's in the wiring of the extension, built 2 years ago with no EIC or any other paperwork! The original wiring is all perfectly fine. So they currently have a radial, which is fine as there's no huge load like a washing machine etc on it, and I'll be going back while they are on holiday next week and try and trace exactly where the problem is. Absolutely perfect values, >1000MOhms on IR and correct continuity values. On the bad section which I've isolated - continuity 40+Ohms and IR values all over the place.

There definitely needs to be some education for customers when extensions etc are built. They must insist on the correct paperwork for any electrical work. I bet in this case it hasn't been notified either.

Having said that though, given the client has had rat issues, this is still the top suspect - a chewed cable.
 

Reply to Rats and tripping MCB in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
539
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
881
Hello I have some decking lights which to be fair, have been nothing but pain in the bottom since they were installed. Moisture in the lens lamps...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock