RCD keeps tripping when I use my grill, why?

Discuss RCD keeps tripping when I use my grill, why? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hello

I have lived in my flat for over 6 years without ANY electrical problems whatsoever. Now, since having a new Wylex consumer unit fitted with RCD's my grill on my cooker keeps tripping the RCD's after it has been on for around 2 minutes. The grill was used every day for the week before so it should have been dry and not damp. also most of the indicator lights on the cooker do not light up now! (the oven and 1 ring light up to show they are on) The rest do not work now. Why is this please?

Before the changeover, my cooker worked fine, never had a problem. I've also noticed my cordless drill charger now does not light up nor does it charge the battery as it did before the change.

Can anyone please shed some light on this matter please? Pulling my hair out and don't need the hassle of having to look at buying a new cooker!

Also fed up of the electricians telling me to "buy a new cooker, that will sort it, your's is obviously broken"

Help? Thanks
Colin.
 
Easy diy way to safely check power feed to socket is to get plug in power monitor. Test your battery charger usage in your flat and round a friends...compare readings

sent from my HTC HD2 using tapatalk
 
the cooker could wellbe damaged, and you didnt know beofre as MCB's are not as sensitive as RCD's. that would explain the grill tripping the RCD. You could get your cooker tested. AS for the lights, didthe spark carry out any testing, and did he switch off the cooker at the isolator during this testing.
 
If a CU change was carried out the installer should have given you an Electrical Installation Certificate which should show a full set of test results and show up any problems. If not you should be getting back to him a demanding one. It is likely that even if a proper set of tests was carried out at the time this would not have included the cooker itself,so if the cooker element has a low insulation resistance...(very common)....an RCD will pick that up where as the protective devices before an RCD was fitted wouldnt. Either way your electrician should be able to pinpoint the cause with proper testing.
The charger issue is a bit odd....again,testing of the socket will pinpoint any issues there. It is possible that if your electrician carried out L-N 500v insulation tests at the time of the CU change and didnt disconnect the charger (and perhaps cooker lights?) some damage has been done to it. I would stress "possible" though.....most electricians know not to carry out such a test for exactly that reason,and IR tests are usually carried out in a way that cant do any damage.
 
Last edited by a moderator:
The element in the grill is probably breaking down prior to failing completely.
It's very common for an RCD to "find" heating elements on their way out.
Kettles are favourite.
Replace the element in your grill And you more than likely solve the problem.
(they're about £20).
 
The element in the grill is probably breaking down prior to failing completely.
It's very common for an RCD to "find" heating elements on their way out.
Kettles are favourite.
Replace the element in your grill And you more than likely solve the problem.
(they're about £20).

This is exactly what i had to do after a board change, oven kept tripping the RCD after it had been on for about 5 minutes , £20 and a new element later not had a problem since.
 
the element is the most likley cause element inside is basicaly a spring and when heated it will expand at different rates due to hot spots ect over the years and this is probably the cause of your problem wouldnt show up on MCB but as has been said RCBOs tend to find these sorts of things
Fluff on a steam iron is another thing that does it
 
Excessive toast crumbs lying in the bottom of toaster.
Any sort of leakage caused by dampness creeping into fittings.
Irons - full stop
Portable electric heaters - full stop

Hopefully you get the idea. The RCD gives you a higher level of protection and is really a fantastically clever device. You can get "nuisance" tripping but the benefits outway the drawbacks by an order of magnitude.
 

Reply to RCD keeps tripping when I use my grill, why? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock