R
Ross Trician
Evening all. I changed a consumer unit last week (was an old wylex one that was "broken" and unsafe)
There were a few problems/faults on the circuits some of which were easily rectified others need further work (if customer will pay for it etc)
My question is this, on the "house sockets" circuit there is a neutral/earth short and when this is connected to the c/u on the rcd protected side it holds the rcd in and wont allow it to trip, (rcd trips fine when circuit is disconnected) why does this occur? I rang wylex technical and might aswell of asked someone in macdonalds.....they were clueless and helpless...was very disapointed in there help.
the thing that concerned me is lets say you do a full rewire and al circuits are fine etc on completion some time later someione puts nail thru the cable and touches Neutral and earth (same as fault now on my circuit) this would then cause the rcd to not trip if a cable was cut for axample.
Also, usaully if you touch neutral/earth together rcd trips but not in this case. why??
can't get my head round this one....help/advice appreciated.
Ross
There were a few problems/faults on the circuits some of which were easily rectified others need further work (if customer will pay for it etc)
My question is this, on the "house sockets" circuit there is a neutral/earth short and when this is connected to the c/u on the rcd protected side it holds the rcd in and wont allow it to trip, (rcd trips fine when circuit is disconnected) why does this occur? I rang wylex technical and might aswell of asked someone in macdonalds.....they were clueless and helpless...was very disapointed in there help.
the thing that concerned me is lets say you do a full rewire and al circuits are fine etc on completion some time later someione puts nail thru the cable and touches Neutral and earth (same as fault now on my circuit) this would then cause the rcd to not trip if a cable was cut for axample.
Also, usaully if you touch neutral/earth together rcd trips but not in this case. why??
can't get my head round this one....help/advice appreciated.
Ross