Search the forum,

Discuss RCD not tripping in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

S

smiffy

Last month I changed a consumer unit and all was well. Now neither of the RCD's are tripping correctly. I get either >50v or >40ms. Could this be 2 faulty RCD's? the make is Contactum and the elecsa guy I spoke to today didn't seem too keen on them. Idea's most welcome
Carl
 
what tester? try testing RCDs at the RCD with the associated MCBs OFF.
 
Bloody Contactum..... 2 lazy/faulty RCD's on the same board. Changed them out , new ones working ok. Never fitting Contactum again.
 

Reply to RCD not tripping in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock