Hello. I am looking into the wiring loom of my 53 year old car and the fitness of the wires and connectors within. I have the two part loom that runs from the rear lights to the fuses under the bonnet out, and have been measuring the resistance of each line. Question is; what would be considered too high? A new cable of the same size and length gives me 0.7 ohms, but I am getting various readings up to 5ohms. I would presume that the higher the resistance the dimmer the light. So where should I draw the line and consider replacing with new wire? Thanks. Andrew
 
The resistance of wire does not increase with time, unless the copper is completely corroded through by chemical action (in which case your car is probably at the bottom of the sea.) If you are reading high resistances it is probably due to faulty connections and remaking those, onto clean bare copper, will sort out the problem. It is even possible that the connectors themselves are OK but your multimeter probes are not making great contact with them due to surface tarnish. Grip the loom wires with sharp-toothed alligator clips and see what you get. Often with the very low test voltage that a multimeter uses, you will see extra resistance from that oxidation that 'disappears' when 12V is applied. E.g. you have a circuit that reads 5 ohms to the multimeter, but when subjected to working conditions, the oxide film breaks down and only the 0.7 ohms of the copper wire remains.

In a nutshell, you need to exactly localise the source of the high resistance, it's unlikely to be the wire itself.
 
The simple go / no-go test is the calculated resistance of the conductor, plus say 10% for manufacturing tolerance, plus say 0.1 ohms each end for terminals / connectors. If you test between terminals and find a resistance that is too high, invariably the problem is failed terminations, not the conductor, so one or both ends needs reworking. The only time you will have to replace actual wiring on account of the conductor is when it is too corroded or too short to re-terminate effectively.

But before you condemn anything, double-check your meter lead contact with the terminal and your null setting for the leads. I spend a lot of time doing this sort of test and I would say 80% of the times I glance at the multimeter and see a high reading, it's because I haven't managed to make good contact with the connector insert or terminal.
 

Reply to Resistance in loom wires in the Auto Electrician Forum area at ElectriciansForums.net

Similar Threads

Hello, disclaimer: this is DIY and I am rather ignorant about electrical works. I just moved into a new rental apartment and i wanted to connect...
Replies
11
Views
515
I am wiring up a new kitchen and conservatory. I'm not sure why I checked continuity between line and the metal back box of the light switch, but...
Replies
3
Views
734
I am adding a light fixture in a room I am restoring in my 160 yo house. I have ran a new 12-2 w/ground wire from the ceiling box to a junction...
Replies
2
Views
881
can anyone please advise on where the wires go? My electrician installed a new cable ready for when I bought a security light. The cable as shown...
Replies
3
Views
548
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock